Nothing in this will be enforceable for a code official. The only thing that matters is what is written in the codes adopted in your area. Instead of looking at this type of web page you would be better advised to talk to your local code enforcement official.www.ajfire.org/uploads/smoke_alarm_requirments.pdf
I have not read it yet but it has all 50 states in it.
Thank you JW I will do that.Nothing in this will be enforceable for a code official. The only thing that matters is what is written in the codes adopted in your area. Instead of looking at this type of web page you would be better advised to talk to your local code enforcement official.
I can tell you with complete confidence that installing smoke alarms in each unit supplied by the house panel is a NEC violation.
Yes you are correct, my badquote; detection devices are not interconnected and must have a control panel.
They ARE "interconnected" but each one has a "address" and the control panel is usually "polling" them to check their status.
I will, tried calling him today but he is out of town.quote;
installing smoke alarms in each unit supplied by the house panel is a NEC violation.
Let us know what you find out, because this statement, if true, would be one of the most illogical requirements I have ever heard.
Ah, JW this is one building with 3 small units one above the other.Where more than one building
or other structure is on the same property and under
single management, each additional building or other structure
that is served by a branch circuit or feeder on the load
side of the service disconnecting means shall be supplied
by only one feeder or branch circuit unless permitted in
225.30(A) through (E). For the purpose of this section, a
multiwire branch circuit shall be considered a single circuit.
Who cares what they want to see all that matters is what the code says. Even if the inspector signs off on an installation the installer is still liable for the installation
Each unit being a structure due to the required fire rating then only one feeder or one branch circuit is allowed to serve any one unit. Each unit will have a different address such as street number and A, B or C.Ah, JW this is one building with 3 small units one above the other.
I understand, but this an in house only systemEach unit being a structure due to the required fire rating then only one feeder or one branch circuit is allowed to serve any one unit. Each unit will have a different address such as street number and A, B or C.
The only other way around this is to have one panel serve all the units
Each unit being a structure due to the required fire rating then only one feeder or one branch circuit is allowed to serve any one unit. Each unit will have a different address such as street number and A, B orAh, JW this is one building with 3 small units one above the other.
I understand, but this an in house only system
and not connected to any fire alarm control that would send a signal to 911 so the address issue is moot.
This is awkward, but...