Silicone Coulping to PVC Male Adapter?

Discussion in 'Shower & bathtub Forum & Blog' started by jsarin1, Sep 26, 2010.

  1. jsarin1

    jsarin1 New Member

    Messages:
    21
    Location:
    Naperville, IL
    I have a tub drain installed to 1.5" PVC Male Adapter via a 1.5" silicone flexible coupling.
    It is tightened down well enough to where it is not leaking. I filled the tub to capacity and allowed it to drain and still there are no leaks. Will this setup hold-up well over time?

    I included a makeshift diagram of what i did...

    Attached Files:

  2. jimbo

    jimbo Plumber

    Messages:
    8,997
    Location:
    San Diego
    Not an approved connection for two reasons:
    ► although you seem to have no leaks, the manufacturer defintely specifies that coupling for use on a smooth pipe, not on threads.
    ► a coupling like that should not be in an inaccessible location. The drawback with it is that if you ever have to cable the drain, the head of the snake may poke through the rubber. You need to get rid of the male adapter, and use stainless steel banded flex, with two different ends, one for tubular, one for IPS.

    A plumber would be able to install this without flexible couplings, but at a minimum, you should do it as I described.
  3. dlarrivee

    dlarrivee New Member

    Messages:
    1,172
    Location:
    Canada
    Why on earth would you use a threaded adapter? And beyond that, why use a "silicone" (not silicone) coupling anyways?
    Last edited: Sep 26, 2010
  4. jsarin1

    jsarin1 New Member

    Messages:
    21
    Location:
    Naperville, IL
    I am installing an American Standard tub with an overflow that's mounted at an angle from the existing plumbing, so I used the flexible coupling for some flex. But, I think I'm going to re-do this...thank for the quick reply guys...
  5. hj

    hj Moderator & Master Plumber Staff Member

    Messages:
    26,636
    Location:
    Cave Creek, Arizona
    The overflow MAY be on an angle, (but I have never seen one like that), but the pipe coming down from the drain tee is NOT at an angle. That "Fernco" coupling is not meant to fit over threads, and is not intended for use ANYWHERE inside a building.
Similar Threads: Silicone Coulping
Forum Title Date
Shower & bathtub Forum & Blog Color matched 100% silicone for Mapei Ultra Color Plus May 26, 2014
Shower & bathtub Forum & Blog Shower surround - horrible mess with silicone caulk May 8, 2013
Shower & bathtub Forum & Blog silicone caulk is not sticking to acrylic tub surface. Aug 26, 2012
Shower & bathtub Forum & Blog where to buy real silicone caulk, preferably colored Jun 13, 2012
Shower & bathtub Forum & Blog Exactly how much does "all" mean when removing old silicone Feb 7, 2011

Share This Page