    We have a shallow point driven well in northern Wisconsin. The pump/well had been working fine; however, the pump cracked this past winter (possible freeze?) and we are having trouble priming the system.

    We have installed a new 1" pipe inside the original 2" pipe, installed a new pump and pressure tank. The bottom of the point is approximately 32ft. from top of pipe with 11ft - 14ft of water in the pipe. We had poured 15 gallons of water in the pipe and it disappears as quickly as we could pour it into the pipe (appears screens on point are clear). We piped up the entire system, new pump, 1" line in well pipe, new 20 gallon pressure tank, new piping (except for check valve) and can not get it to prime. Pressure gauge in the line goes up to 30 psi and no further with pump running.

    We did not install a foot valve in the 1" pipe, wanting an option to drain the pipe in the future, with the cold Wisconsin winters. We do have a check valve before the pump as the piping comes out of the well pipe.

    Any suggestions of what to try? Could the check valve be bad? It was new last fall and we reused from previous set-up.

    It makes no sense to have the amount of water we have in the pipe and not be able to prime the pump.
  2. Wet_Boots

    Wet_Boots Sprinkler Guy

    Messages:
    798
    Location:
    Metro NYC
    Are you restricting the pump's discharge? There has to be considerable losses in the undersized suction pipe, and that can't help your attempts to prime.
  3. mmiller4

    mmiller4 New Member

    Messages:
    2
    Location:
    Wisconsin
    What type of restriction do you mean? Sizing down the piping to the house or shut off valve being closed? Out of the pump we go to 3/4" piping to pressure tank and ball valve out of pressure tank to house. Ball valve is closed when trying to prime pump?
  4. speedbump

    speedbump Previous member

    Messages:
    4,540
    Location:
    Riverview, Fl.
    Are you leaving the priming plug loose when priming to let air out?

    bob...
  5. Wet_Boots

    Wet_Boots Sprinkler Guy

    Messages:
    798
    Location:
    Metro NYC
    I'd be closing a shutoff valve between the pump and house, and using another outlet upstream of that shutoff to work the flow as I primed the pump. For some reason, when there's a restriction on the suction side of the pump, the priming is more difficult, and you need to tweak the flow, while you get all the air out of the pump. Once you have it primed, then you can slowly open the valve to the house.
Similar Threads: Shallow pump
Forum Title Date
Plumbing Forum, Professional & DIY Advice shallow well jet pump mystery Oct 20, 2009
Plumbing Forum, Professional & DIY Advice shallow well-pump to well head distance Jan 22, 2009
Plumbing Forum, Professional & DIY Advice Options for Shallow Sink Over Dishwasher Sep 18, 2010
Plumbing Forum, Professional & DIY Advice screen in shallow wells Jul 15, 2010
Plumbing Forum, Professional & DIY Advice Shower valve roughed in just a bit too shallow Sep 7, 2008

Share This Page