Sewer line pipe size

Discussion in 'Plumbing Forum, Professional & DIY Advice' started by Terry, Jun 7, 2005.

  1. Terry

    Terry Administrator Staff Member

    Joined:
    Aug 17, 2004
    Occupation:
    Plumber
    Location:
    Bothell, Washington
    Posted for Gene

    am disconnecting from septic tank to hook up into sewer line--what size pipe is best--i will have 2-45 degree turns from old septic tank to hit sewer line--would i need 2 clean out pipes at those turns--any advice appreciated--gene thanks
     
  2. hj

    hj Moderator & Master Plumber Staff Member

    Joined:
    Aug 31, 2004
    Occupation:
    Plumber
    Location:
    Cave Creek, Arizona
    pipe

    Use whichever size is coming from the house and put the two cleanouts at the house, opposing each other, so the one closest to the house points towards the septic and the further one points back to the house.
     