Running 2 Taco zone pumps off one Taco controler

Users who are viewing this thread

Tom3holer

Member
Messages
63
Reaction score
0
Points
6
Location
Cape Cod
Hi,

I just had a new heating system installed in my home. It is a boiler/baseboard system with 5 zones.
I have now discovered the installer really didn't have a clue as to what I really needed. He did no heat loss study and just assumed the old boilers rating was what I needed. I have ended up with a system that is probably 2x the BTU's that I need which causes it to short cycle much of the time.
One of the things I have read that I can do to help this expensive screwup is to have more heat load. If I combine two of the three zones on the first floor that should help. Does anyone know if you can run two Taco 007-FS-71FC punps from one zone on a Taco SR-504 zone controler?

Thanks,

Tom
 

ShockHazard

New Member
Messages
50
Reaction score
0
Points
0
Location
North East Pennsylvania
You can pull up to 1/3 hp per zone on that controller.
I'd reccomend simply getting a larger pump.

Your pumps are 1/25 hp.

Make sure the temperature ranges on the aquastat are set far apart - this will reduce cycling and often add to efficiency.
 