I'm relocating my dryer outlet (3-prong), and am replacing the ROMEX® with a longer run (need about 3 more feet). Need to buy the right ROMEX®.

The existing ROMEX® is 10/2 with insulated ground. Is having an insulated ground important? Seems that the 10/2 w/ground I saw at the store had a bare ground wire, but I could be mistaken. Just want to buy the right stuff. Thanks. :)
 
Last edited by a moderator:

CodeOne

Code Enforcement
Messages
160
Reaction score
0
Points
0
Location
North Carolina
In your other post you accepted the GFCI from the 2008 Nec. Something else that change is the range and dryer circuits. They now have to be 4 wire instead of 3 wire.
See Article 250.140 below

Frames of Ranges and Clothes Dryers. Frames of electric ranges, wall-mounted ovens, counter mounted cooking units, clothes dryers, and outlet or junction boxes that are part of the circuit for these appliances shall be connected to the equipment grounding conductor in the manner specified by 250.134 or 250.138.

Exception: For existing branch circuit installations only where and equipment grounding conductor ia not present in the outlet or junction box, the frames of wall-mounted ovens, countermounted cooking units, clothes dryers, and outlet or junction boxes that are part of the circuit for these appliances shall be permitted to be connected to the grounded circuit conductor if all the following conditions are met.
(1) The supply circuit is 120/240-volt, single-phase,
3-wire; or 208Y/120-volt derived from a 3-phase,
4-wire, wye-connected system.
(2) The grounded conductor is not smaller than 10 AWG
copper or 8 AWG aluminum.
(3) The grounded conductor is insulated, or the grounded
conductor is uninsulated and part of a Type SE service entrance
cable and the branch circuit originates at the
service equipment.

(4) Grounding contacts of receptacles furnished as part of
the equipment are bonded to the equipment.

So if you are replacing the circuit, most jurisdictions would require you to run 10/3 with a ground to your dryer, and make sure you separated the bonding strap from the grounded conductor in the dryer.

10/3 with a ground gives you 2 hots a grounded conductor ( neutral) and an uninsulated grounding conductor.
This makes a much safer installation.
 
Last edited by a moderator:

Plumbob

Member
Messages
30
Reaction score
0
Points
6
Thanks. Yes, I want to do this in compliance with code, and if I read what you provided correctly, I think it says that if wiring to the junction box does not include a separate ground (true) that I can stay with 10/2 w/insulated ground if all those conditions apply (which I believe they do). Thanks again.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
Moving it generally means bring it up to code, so no, you can't just add some wire...you need to rerun it with new so it has the proper ground and neutral, i.e, change the plug to 4-wire and a new run.
 

Frenchie

Jack of all trades
Messages
1,239
Reaction score
0
Points
36
Location
Brooklyn, NY and Fire Island, NY
Thanks. Yes, I want to do this in compliance with code, and if I read what you provided correctly, I think it says that if wiring to the junction box does not include a separate ground (true) that I can stay with 10/2 w/insulated ground if all those conditions apply (which I believe they do). Thanks again.

Nope. He went over your head. Over my head to explain how, probably.

I think you misunderstood which junction box the code's talking about. Some driers (the ones in laudromats for example), instead of a plug & a receptacle, they're wired straight into a junction box.



The basic logic goes:

The wire from the current location, to the new location, is new work.

New work has to be to current code. 12/3 + ground, 2 hots connected to opposite phases, a neutral connected to the bus bar, a ground connected to the ground bar.

That can't be done, junctionning off the old feed, you'd be short a wire. So you have to run a new feed.

The old wire/location, could be re-used for a single-voltage circuit. Something strictly 220 (hottub?), or strictly 110 (junction for some extra receptacles somewhere?).
 

Plumbob

Member
Messages
30
Reaction score
0
Points
6
I think I understand now. BTW, the "junction box" is a small metal work-box attached to a beam in my utility room. All that's inside it is a splice (3 wire nuts) connecting two runs of 10/3. I'm not even sure why its there. Maybe the dryer was relocated years ago before I owned the house.

I can't justify busting up walls in my finished basement to install a new line back to the panel, just to move the dryer outlet a couple feet, so I'll live it as-is. The dryer cord reaches it, but I was just going to move it a bit closer.

Final question, I haven't installed a new dryer, its the same one I've had for years (with a 3-prong plug). But if I did buy a new dryer would I have to install a new outlet and wire run back to the panel, or would I just buy a cord/plug to attach to the dryer, and plug it in? I assume dryers don't come with cords, as this one didn't 20 years ago when I bought it.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
I think I understand now. BTW, the "junction box" is a small metal work-box attached to a beam in my utility room. All that's inside it is a splice (3 wire nuts) connecting two runs of 10/3. I'm not even sure why its there. Maybe the dryer was relocated years ago before I owned the house.

I can't justify busting up walls in my finished basement to install a new line back to the panel, just to move the dryer outlet a couple feet, so I'll live it as-is. The dryer cord reaches it, but I was just going to move it a bit closer.

Final question, I haven't installed a new dryer, its the same one I've had for years (with a 3-prong plug). But if I did buy a new dryer would I have to install a new outlet and wire run back to the panel, or would I just buy a cord/plug to attach to the dryer, and plug it in? I assume dryers don't come with cords, as this one didn't 20 years ago when I bought it.

With over 42 years of experience making electrical installations and 10 years of talking on a daily basis on current flow I have but one suggestion.

If you have a dryer or range that is wired with a three wire receptacle no matter the cost have it changed to a four wire receptacle supplied with a three wire with ground circuit as soon as possible.

With a three wire receptacle the case (anything metal) is energized to the same level as the voltage supplying one half of the appliance. In the event of unintentional contact with a different potential severe damage or even death can occur to the human body.

Not long ago I was involved in a case where the house wife was using her husband’s finder cover on the dryer door so she wouldn’t be shocked while putting wet cloths from the washer to the dryer. The dryer had a three wire receptacle where the bare neutral from the SE cable was loose and while the light in the dryer was on the case of the dryer was energized to a level of 120 volts. When she reached into the washer while touching the dryer she received a shock.

Replacing the receptacle and branch circuit supplying the dryer to a 3 wire with ground cured the problem.
 

Jar546

In the Trades
Messages
424
Reaction score
0
Points
0
Location
USA
Website
www.inspectpa.com
With over 42 years of experience making electrical installations and 10 years of talking on a daily basis on current flow I have but one suggestion. Ego statement!


Not long ago I was involved in a case where the house wife was using her husband’s finder cover on the dryer door so she wouldn’t be shocked while putting wet cloths from the washer to the dryer. The dryer had a three wire receptacle where the bare neutral from the SE cable was loose and while the light in the dryer was on the case of the dryer was energized to a level of 120 volts. When she reached into the washer while touching the dryer she received a shock.

Replacing the receptacle and branch circuit supplying the dryer to a 3 wire with ground cured the problem.
Tightening the connection would have also cured the problem but you can't make money that way can you?

Keep beating your chest
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Tightening the connection would have also cured the problem but you can't make money that way can you?
Keep beating your chest
You sure are trying your best to prove that you have absolutely no knowledge of electron flow at all with statements such as what you have made in the past few days.

For what it is worth I didn’t make a dime off this repair simply due to the fact I didn’t do the installation but instead referred that it be addressed by someone of their choice. They couldn’t afford to pay me to crawl around under their house as I don’t work cheap. I didn’t charge for the service call and finding the problem because it was for a student.
Just where did you come up with the fact that I did the repair in the first place?

For someone who is out for all the safety that you have made it clear that you are looking out for you sure pick some pretty strange ways of showing this concern for public safety.

For any three wire range or dryer the case of the appliance is bonded to the neutral conductor. Each of these two appliances has 120 volt circuits installed within their makeup. Both have 120 volt lights and timing devices. Most dryers have 120 volt motors that turn the tub.

This means that the metal cases of these appliances are bonded to a conductor that is120 volts above anything that is grounded. In the event of the neutral coming loose or being damaged by a rodent and a person coming into contact with the metal case of one of these appliances they become a parallel path for the return current.

This same appliance wired with a four wire receptacle the case of the appliance is bonded to the equipment grounding conductor and should the potential of the metal be elevated it has a low impedance path back to the source and the overcurrent device opens.
 

Jar546

In the Trades
Messages
424
Reaction score
0
Points
0
Location
USA
Website
www.inspectpa.com
Did you guys from NC have a pow-wow before you decide to double team me?

Nothing wrong with tightening a loose connection on a circuit that was completely code compliant when it was installed. Do you change the main panel too when the bond screw gets loose? Still safe.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Did you guys from NC have a pow-wow before you decide to double team me?

Nothing wrong with tightening a loose connection on a circuit that was completely code compliant when it was installed. Do you change the main panel too when the bond screw gets loose? Still safe.


No my young friend no one is trying to double team you at all. With your comments through out the discussion form for safety you sometimes chew on the other side.

A history quesiton for you should you decide to accept it.

What years was a three wire receptacle compliant for a range and dryer?
 

Alectrician

DIY Senior Member
Messages
688
Reaction score
0
Points
0
The existing ROMEX® is 10/2 with insulated ground. Is having an insulated ground important? Seems that the 10/2 w/ground I saw at the store had a bare ground wire, but I could be mistaken

The insulated ground isn't the real issue.

Combing the ground and neutral on the same wire is the real issue.



NEC says:

New circuits must be 3 wire with ground.

Existing circuits can still use the 2 wire with ground setup (SE cable).





Relocating an existing 2 wire circuit isn't addressed in the NEC and is a gray area in most locations. I have never seen or heard of it being disallowed here.

I strongly suggest a new circuit but..............

If you choose to extend the original 2 wire circuit, make 100 percent sure that the bare wire connection is absolutely tight/secure/bulletproof. If this connection fails, someone is very likely to get killed from the 120V motor current flowing thru the dryer frame, looking for a path to ground.
 
Last edited by a moderator:

Alectrician

DIY Senior Member
Messages
688
Reaction score
0
Points
0
Although it may be technically incorrect, it is the best way to explain it.

The electrons push their way into the load and back to the source, which is grounded.

These electrons want to go to ground and will take the easiest path.

If the designed path is not available for them due to a broken wire/open connection, they look for another way out, like someone touching the washer and dryer at the same time and they will take that path at the speed of light.
 