Rinnai tankless popoff valve problem

Discussion in 'Tankless Water Heater Forum' started by BrianWitty, Oct 22, 2013.

Thread Status:
Not open for further replies.
  1. BrianWitty

    BrianWitty New Member

    Messages:
    5
    Location:
    Ky
    Hey guys, new to the board...

    I have a rinnai tankless outdoor gas unit (the big 9.4 gpm one) anyway, it's been installed about 2 years now with no real problems. All of the sudden yesterday, I noticed a big puddle in the yard. The popoff valve was pouring water on the ground like it was a garden hose. I turned off the unit and it stopped. I pushed in the popoff felt a click, and turned it back on. Turned on the shower and had hot water, and the popoff wasn't open. Then when I turned off the water, the popoff again opened and started spilling hot water on the ground again.

    Any ideas?
  2. Reach4

    Reach4 Well-Known Member

    Messages:
    2,806
    Location:
    IL
    Failed expansion tank? [​IMG]
    Last edited: Oct 22, 2013
  3. BrianWitty

    BrianWitty New Member

    Messages:
    5
    Location:
    Ky
    Mine is an outdoor unit- attached to the brick. It doesn't have the expansion tank.
  4. Reach4

    Reach4 Well-Known Member

    Messages:
    2,806
    Location:
    IL
    If there is something that keeps water from feeding back to the source, and there increasingly is, you need to add an expansion tank. Was your water meter change recently? It might have added a one-way valve to prevent water from feeding back into the mains. So if your water is coming in at 70 PSI, and it gets heated by the water heater, the water expands. The larger volume of water has to go somewhere.

    I don't know if those popoff valves are made to reset just under the pressure needed to trigger them, but if there is a significant difference in the pressure.

    Of course the problem could be the popoff valve going bad and triggering at too low of a pressure or temperature.
  5. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Messages:
    22,319
    Location:
    New England
    Is that valve designed to open on temperature or pressure or both? If it's temperature, and the burner doesn't turn off when you stop using water properly (flow valve sticking?), it will continue to heat the water , causing it to get REALLY hot, that safety valve should open.
  6. BrianWitty

    BrianWitty New Member

    Messages:
    5
    Location:
    Ky
    I guess changing the popoff will eliminate bad popoff valve... The temp of the water coming of the valve is hot but not really hot- probably 110-115F. I don't don't if the meter was changed, I was out of the country last week and the problem showed up the day we returned.
  7. Reach4

    Reach4 Well-Known Member

    Messages:
    2,806
    Location:
    IL
  8. BrianWitty

    BrianWitty New Member

    Messages:
    5
    Location:
    Ky
    Ok - certainly not opposed to an expansion tank. I did however do another test- I turned the shower on and left it going for about 15 minutes. I went outside to check before shutting the water off and the popoff was open again. Temperature was typical - 115 or so... I think I'll try just a new popoff valve first... Also noticed no change in the water pressure in the shower and the water coming from the popoff did not change significantly after shutting off the shower. Water was not shooting out, just kind of running out. The popoff also was not all the way open, pulling the lever increased the flow quite a bit.

    Cutting power to the heater immidiately stops flow.
  9. Reach4

    Reach4 Well-Known Member

    Messages:
    2,806
    Location:
    IL
    I agree. That was a good test.
  10. BrianWitty

    BrianWitty New Member

    Messages:
    5
    Location:
    Ky
    Problem solved: failed Watts #40 popoff valve. Kinda pissed that an $81 popoff valve failed in just shy of 2 years... Things just aren't made with quality in mind anymore.....
  11. hj

    hj Moderator & Master Plumber Staff Member

    Messages:
    27,258
    Location:
    Cave Creek, Arizona
    The valve should NOT open on temperature rise because the burner should only operate while water is flowing through the heater, but if the valve has weakened, then you are in a "Catch-22", because the valve will open to release the excess temperature, but the water flowing out of it will continue to keep the burner running and the water hot, therefore the valve will never close.
Similar Threads: Rinnai tankless
Forum Title Date
Tankless Water Heater Forum Rinnai Tankless REU-V2520-EFU. Water isn't as warm as it used to be. Feb 7, 2013
Tankless Water Heater Forum Rinnai tankless water heater issues with lg front load washer. Mar 19, 2012
Tankless Water Heater Forum How quiet is a Rinnai tankless, *really*? Feb 22, 2009
Tankless Water Heater Forum Rinnai RC98eP power question. Oct 19, 2014
Tankless Water Heater Forum Rinnai RH 180 Hybrid Dec 6, 2013

Thread Status:
Not open for further replies.

Share This Page