Restricted flow in radiant floor

Discussion in 'Plumbing Forum, Professional & DIY Advice' started by Repair Man Rex, Jan 27, 2010.

  1. Repair Man Rex

    Repair Man Rex Tenacious Amateur

    Joined:
    Jan 27, 2010
    Location:
    Lovettesville, VA
    I am starting up a new radiant floor system which seems to have flow restrictions in two loops. Water moves through them but very little came out when I tested it. The man who set up the manifolds said with confidence that blockage in the manifold or in the tubes was unlikely and that it must be a kink. Another man installed the tubes but he thinks it was done properly. Since the tubes are not labeled we are heating the house to see which areas don't warm. The real challenge will be to know where the kink or blockage is. Is there a way to determine this without tearing up all the gypsum board below? I plan on opening the manifold to inspect it for problems before I get too carried away. I will also flush the lines for a while. Any advice?
     
  2. johnjh2o1

    johnjh2o1 Plumbing Contractor for 49 years

    Joined:
    Aug 9, 2009
    Occupation:
    Retired
    Location:
    South*East
    Try blowing them out with an air compressor. Hopefully there something in the line and its not kinked.

    John
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Joined:
    Sep 2, 2004
    Occupation:
    Retired Systems engineer for defense industry.
    Location:
    New England
    An IR thermometer or an IR camera would likely show something. How well it could isolate the problem, I don't know, but it will show you where the temperature differences are.
     
  5. Repair Man Rex

    Repair Man Rex Tenacious Amateur

    Joined:
    Jan 27, 2010
    Location:
    Lovettesville, VA
    Thanks for the ideas. As it turns out the designer/installer misdiagnosed the problem. I took the manifold apart and found that the send flow gauges on this model (which he was not familiar with) were screwed in at different depths which affected the flow individually. This gave the impression of a blockage. There was still a lower flow through one loop but we realized that it was also a longer run with more friction loss so we adjusted the valve on each run to give a balanced flow through each. Lesson learned: check the manifold!
     
Similar Threads: Restricted flow
Forum Title Date
Plumbing Forum, Professional & DIY Advice New project questions - Water testing and restricted slopes Jan 14, 2013
Plumbing Forum, Professional & DIY Advice Leaking overflow pipe from combo cylinder Feb 18, 2015
Plumbing Forum, Professional & DIY Advice While I'm draining the tub if I flush the toilet the toilet almost overflows? Feb 12, 2015
Plumbing Forum, Professional & DIY Advice Back flow into water heater Jan 22, 2015
Plumbing Forum, Professional & DIY Advice Bathtub overflow question Jan 21, 2015

Share This Page