I'm planning on putting a Toto UT104 0.5gpf urinal into a bathroom where getting a 3/4" water line is impossible for a few reasons. All I have to work with is 1/2". The valve will be a manual Toto flushometer 0.5gpf. The house is on a well system and pressure at the tank is 30psi at the minimum, but I haven't done any fancy pressure testing at the bathroom. If I install a 2 gallon diaphragm accumulator and run 3/4" line from that to the urinal will this be enough to support the valve flush requirements?

Is there anything else I should consider during this project?


Thanks for the great forum!
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
The flushometer only needs of course, the 0.5 gallons....but it needs an instananeous flow of something like 20 gallons per minute. That is why a 1/2" pipe will usually prove indadequate.

Your accumulator idea is probably the correct approach, and as hj says, keep it close.
 

TR_909

New Member
Messages
2
Reaction score
0
Points
0
Location
Sacramento
Thanks for the sanity check on my idea guys. It may be a while before this is finished, but i'll reply and let everyone how it worked out. I know i'm not the only one wanting to do this.
 