Replacing Leaky Hydronic Zone Valve

Discussion in 'Boiler Forum' started by Kiko, Mar 26, 2011.

  1. Kiko

    Kiko Member

    Joined:
    Jul 20, 2009
    Location:
    Royal Oak, Michigan
    I need to replace a leaky hydronic zone valve on my Burnham gas boiler. The new zone valve comes attached to a copper tee that needs to be sweated on. Since the same copper tee already exists (from the old one), can I just detach the valve from the new copper tee and reuse the old tee? Un-sweating that old tee would be very difficult for me, and cutting it out would require a lot of extra soldering, which I would prefer to avoid if possible.


    zone_valve.jpg
     
    Last edited by a moderator: Mar 27, 2011
  2. Tom Sawyer

    Tom Sawyer In the Trades

    Joined:
    Nov 29, 2010
    Location:
    Maine
    It's probably the tee that is leaking, it needs to be changed
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. Kiko

    Kiko Member

    Joined:
    Jul 20, 2009
    Location:
    Royal Oak, Michigan
    No, it's leaking right out of the valve itself. The tee is fine.
    It would make sense that these valves would twist off from the tee portion to prevent melting the plastic part of the valve when soldering.
    Does anyone know this to be the case, or do I need to call White-Rodgers for the answer?
     
  5. Tom Sawyer

    Tom Sawyer In the Trades

    Joined:
    Nov 29, 2010
    Location:
    Maine
    No, it is leaking out of the stem seal on the valve itself. You need to replace the entire thing.
     
  6. Kiko

    Kiko Member

    Joined:
    Jul 20, 2009
    Location:
    Royal Oak, Michigan
    I talked to the fine folks at White-Rodgers, as well as some local boiler repair guys, and they all said that these hydronic zone valves are designed to be twisted out from the copper tee and replaced in a matter of seconds to avoid a lot of air being sucked into the system. They can also be rebuilt (new seals, new valve assembly, new motor) all without having to remove the copper tee.
     
  7. Tom Sawyer

    Tom Sawyer In the Trades

    Joined:
    Nov 29, 2010
    Location:
    Maine
    Yes, sorry, I was not being clear enough. You will need to shut the system down, drian the pressure and then remove the motor and the valve body from the tee. It's leaking from the stem seal. which is why I said the tee.
     
Similar Threads: Replacing Leaky
Forum Title Date
Boiler Forum Replacing electric boiler with gas. need piping help Aug 25, 2015
Boiler Forum Replacing Cast Iron Burnham Mar 7, 2015
Boiler Forum Replacing head and internal screen on spirovent Feb 28, 2015
Boiler Forum Help Replacing an Old Boiler Sep 14, 2014
Boiler Forum Replacing old NG boiler / water heater - check my sizing please? Sep 6, 2014

Share This Page