    The prevous owner had some flourescent lights hard wired in the closets of our home. These light assemblies are about 42" long and contain 2 ea F13T5 bulbs, about 20" long. They are giving out and replacing the bulbs doesn't help, so it must be the ballasts! Tried to buy the ballasts locally, to no avail, so I ordered some off the internet. The orig ballasts have a p/n E2813NP on them, Electronic Ballast, for (2)F8T5 and/or F13T5 lamps. There are blk & wh power wires exiting the case, along with 4 red & 4 blue wires for the flour. lamps. The ballast I received is a solid state electronic ballast, for T5, T8 & 2x F21T5 lamps. The sales slip accompaning them says Fulham Workhorse long case ballast, WH2-120-L, operates (2) F13 T5 lamps. But, other than the B&W power wires, there are 2 red and 1 yellow wire exiting the case. While the old ballasts have a wiring diag on the case, the new ones don't, and I'm at a loss as to how to wire them.:mad:
     
  2. jimbo

    jimbo Plumber

    Joined:
    Aug 31, 2004
    Location:
    San Diego
    The new ballast should come with a wiring diagram. You may need to reconfigure the wiring to the tombstones.


    Here are the instructions:
    Diagrams for T5 Linear with a bulb set 2xF13

    Diagram 1 for Workhorse 2 Diagram 1 for Workhorse 4 Diagram 1 for WHAM 2 Diagram 1 for Longhorse 2 Diagram 1 for Longhorse 4 [​IMG]
     
    Last edited: Dec 2, 2008
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. Malibu Jim

    Malibu Jim New Member

    Joined:
    Oct 18, 2007
    Location:
    California
    Thanks. The ballasts came w/o any schematic, but I should've thought :)about checking the mfg web site.
    Thanks again
     
  5. jar546

    jar546 In the Trades

    Joined:
    Feb 20, 2008
    Location:
    USA
  6. Cass

    Cass Plumber

    Joined:
    Nov 12, 2005
    Location:
    Ohio
    Just curious if they are required on residential...
     
  7. hj

    hj Moderator & Master Plumber Staff Member

    Joined:
    Aug 31, 2004
    Occupation:
    Plumber
    Location:
    Cave Creek, Arizona
    code

    The specification states for non-residential use.
     
  8. jwelectric

    jwelectric Electrical Contractor/Instructor

    Joined:
    Jun 14, 2007
    Occupation:
    Instructor
    Location:
    North Carolina
    (G) Disconnecting Means.
    (1) General. In indoor locations other than dwellings and associated accessory structures, fluorescent luminaires that utilize double-ended lamps and contain ballast(s) that can be serviced in place shall have a disconnecting means either internal or external to each luminaire. The line side terminals of the disconnecting means shall be guarded.

    I don't think so
     
  9. jar546

    jar546 In the Trades

    Joined:
    Feb 20, 2008
    Location:
    USA
    This is true.....
     
  10. jwelectric

    jwelectric Electrical Contractor/Instructor

    Joined:
    Jun 14, 2007
    Occupation:
    Instructor
    Location:
    North Carolina

    But still a good idea in my opinion
     
  11. jimbo

    jimbo Plumber

    Joined:
    Aug 31, 2004
    Location:
    San Diego
    Just curious....with respect to this disconnect plug, and the code, would all the following fall under the "residential" defintion:

    apartment building ( small ones. multistory ones.)
    hotel rooms
    office, lobby, or public spaces in hotel
    laundry room at a condo complex
    a house now permitted as a 6-person assisted living facility.


    Just want to have a feel about how broad the application of this code section is.
     
  12. jwelectric

    jwelectric Electrical Contractor/Instructor

    Joined:
    Jun 14, 2007
    Occupation:
    Instructor
    Location:
    North Carolina
    In NC these would be commercial buildings and the disconnect for lights with ballast would require a disconnect
     
Similar Threads: Replacing Flourescent
Forum Title Date
Electrical Forum discussion & Blog Replacing Emergency light Jul 10, 2015
Electrical Forum discussion & Blog Replacing Romex with MC flex cable - boxes and connections Feb 14, 2015
Electrical Forum discussion & Blog Replacing light switch with a Timer that has an extra Red Wire. Jan 24, 2014
Electrical Forum discussion & Blog Ignorant question, business replacing receptacles and switches. Oct 28, 2013
Electrical Forum discussion & Blog Problems replacing old GFCIs Nov 27, 2010

Share This Page