I need to replace a small section (about 3 feet) of horizontal 3" Copper waste line. This is part of a longer run (about 10 feet), but only a small section has been damaged. I was planning to use Fernco Proflex transition couplings (#3001-33) to replace it with PVC. These are specifically designed for the 3" copper vs 3" PVC size difference.
My concern is that with the PVC being larger than the copper, this will create a 3 foot section of "lower" area within the piece of PVC for waste to collect. Is this an issue or is the size difference not enough to cause a concern? I found online that 3" copper (L) ID is 2.945" and 3" SCH 40 ID is 3.042". However the copper wall thickness is .090 and PVC is .216...maybe the wall thickness difference will make them align pretty well?
Thanks!
My concern is that with the PVC being larger than the copper, this will create a 3 foot section of "lower" area within the piece of PVC for waste to collect. Is this an issue or is the size difference not enough to cause a concern? I found online that 3" copper (L) ID is 2.945" and 3" SCH 40 ID is 3.042". However the copper wall thickness is .090 and PVC is .216...maybe the wall thickness difference will make them align pretty well?