recirc system

Users who are viewing this thread

Plumberwanabe

New Member
Messages
9
Reaction score
0
Points
1
Location
Bellevue WA.
I'm interested in installing a hot water recirculation system, with a dedicated return line. The dedicated return line will be made of 1/2" pex. What should I look for in a pump? Should I make the return line enter the hot water tank at the cold supply side with a check valve? Or is there a better design for the return water? The system will have 5 or 6 feet of head. What's a good brand name of pump?
 

hj

Master Plumber
Messages
33,599
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
Regardless of where you connect it back, cold water inlet or drain valve, it MUST have a check valve. Almost any pump is adequate since the only "head" will be caused by the water's velocity, but you want the water to flow as slowly as possible and still maintain the temperature.
 

Terry

The Plumbing Wizard
Staff member
Messages
29,946
Reaction score
3,460
Points
113
Location
Bothell, Washington
Website
terrylove.com
Grundfos makes a nice pump, and also an optional "clip on" that shuts the pump off when the return comes back warm. It keeps the pump from running non-stop.

I like to pull and extend the water heater drain and run the recirc in there. I use a spring check.

I wound up parking at city hall Wednesday while Jamie was playing Bellevue City Center.

live_at_lunch_5078.jpg
 
Last edited:

Gary Swart

In the Trades
Messages
8,101
Reaction score
84
Points
48
Location
Yakima, WA
Here's how my system is plumbed. Not the only way, but it's worked well for me for about 8 years. The return line reached the area of the tank at just a bit above floor level. The first fitting is a ball valve. Then the line runs into the Laing pump. After the pump, there is a tee. One side of the tee goes to the floor drain, the other directs the pipe up to just above the top of the tank. Now the pipe elbows toward the tank and through a check valve. Following the check valve, there is an air vent. Another ball valve follows the air vent and then the pipe is teed into the incoming cold water pipe. I elected not to have a timer, but that is an option many people prefer. I use all copper and the hot water lines, including the return line, are insulated. I'm not a fan of PEX, but it would probably work just fine.
 

Hairyhosebib

New Member
Messages
172
Reaction score
0
Points
0
Location
Arizona
A check valve is needed but get one used in the solar hot water industry. One that may only need a half pound of pressure to open it. You can get a Grundfos circ pump that may only be 1/64 of a HP. That be just about nothing in electrical use. It just keeps the water moving. I would extend the drain and make the tie in at the bottom of the tank. Hopefully your tank is not full up to that point of accumulation of crap. If you have filtration and a condition system of some kind it should be good for a long time. Otherwise junk might build up in the check valve and it will drive you nuts that it does not work very long.
 