    How close can electrical outlets for washer (110v) and dryer (220v) be to the washer hookup valves?
    The laundry tub is nearby too... What are the electric outlet positioning requirements? Thanks.
  2. Jim Port
    Jim Port Electrical Contractor
    Aug 22, 2009
    Maryland
    There are no code imposed limits on the promity of the receptacles to the valves.
    If the washer receptacle is within 6' of the laundry tub it requires GFI protection.
    [​IMG]
  4. jwelectric
    jwelectric Electrical Contractor/Instructor
    Jun 14, 2007
    Instructor
    North Carolina
    I agree with this post but let me add that they can be no more than 6 feet from the appliance they intend to serve.
    210.50(C) Appliance Receptacle Outlets. Appliance receptacle outlets installed in a dwelling unit for specific appliances, such as laundry equipment, shall be installed within 1.8 m (6 ft) of the intended location of the appliance.
  5. hj
    outlets
    I believe, since this is the way they are usually installed, that as long as the receptacles for a washer and dryer are "filled" it does not have to be a GFCI. This means if you have a washer and electric dryer, the outlet has to be a single device one so there is no "open" receptacle where you could plug an extension cord or device into.
  6. jwelectric
    Jun 14, 2007
    Instructor
    North Carolina
    Even a single device yoke within 6 feet of a utility tub would require GFCI protection
  7. hj
    Gfci
    They did not put one there for my installation, I just looked to make sure I was not mistaken. The same applied for my water softener outlet in the garage. ALL the wall outlets in the garage are GFCI, but the softener is a single device receptacle and NOT GFCI protected.
  8. Scuba_Dave
    Scuba_Dave Extreme DIY Homeowner
    Jan 5, 2009
    Used to be in IT
    South of Boston, MA
    They used to have exemptions for dedicated point of use
    NEC 2008 did away with them
    Within 6' of a sink should have been GFCI before
    I have GFCI protection on every outlet in the laundry area
  9. Speedy Petey
    Speedy Petey Licensed Electrical Contractor
    Jun 16, 2007
    NY State, USA
    Also, a "filled" receptacle is certainly NOT an excuse or exception to requiring GFI protection or not.
    The old exception was if a receptacle was behind a "large" appliance not easily moved. As was stated, this exception was removed from the code.
    Your softener is not and never was legal if the receptacle was installed within the last 20-25 years or so. I will admit, this is something often overlooked by inspectors, not that that makes it right.
  10. hj
    receptacle
    NOT having a dedicated receptacle be GFCI eliminates the possibility of a "false trip", especially if it is for something "critical" such as a freezer which might go for days without discovery, or at least until the odor become overpowering. And I have know many people it happened to, including my daughter. And a customer who had it happen and did not know the GFCI was UNDER a bench in their bathroom, so they just assumed it was a bad outlet and ran an extension cord to the freezer, until MONTHS later when I told them it was probably a tripped GFCI and hunted it down. If the device is plugged into a single device outlet, it is unlikely it would be unplugged to use for an extension cord connection point.
  11. Speedy Petey
    Jun 16, 2007
    NY State, USA
    OK, but do you have a code citation to support this opinion?
    See my point?
    The code making panels obviously disagree with this opinion since they removed most all exceptions for GFI's in unfinished areas.
    Besides, nuisance tripping GFI's really are becoming a thing of the past.
  12. jar546
    jar546 In the Trades
    Feb 20, 2008
    USA
    If you are under the 2008 NEC then GFCI protection is mandatory, PERIOD.
    About 10-12 years ago the appliance manufacturers were mandated to provided equipment that had leakage current of less than 2mA. This is not even close to what it would take to trip a GFCI. The new generation of appliances and GFCI protection is not a problem.
    A smart person will put a light/LED in series with the GFCI receptacle that will let you know the condition of the GFCI OR they can use a GFCI that is visible and illuminates a small LED when the power is off at the receptacle from a trip.
  13. Scuba_Dave
    Jan 5, 2009
    Used to be in IT
    South of Boston, MA
    I actually do have an outlet behind the freezer in the basement that might not be GFCI
    I can't really get to it at all unless I unload & move the freezer
    But since the outlet was there prior to 2008 code I guess it's OK
    I haven't looked at that outlet since we moved in 6 years ago
  14. jetlag
    jetlag New Member
    Dec 12, 2009
    Ga.
    We have all heard a story about the food in a freezer in a basement, good argument but it wont cut the mustard with the code or inspectors any more. All recepts in unfinished basement or within 6 ft of a sink must be GFCI. Even the washer and garage door opener in the ceiling.
  15. Plumbob
    Plumbob Member
    Jun 13, 2005
    Thanks everyone. I bought a 3-pack of GFCI outlets so all the outlets in my unfinished laundry room will be GFCI, along with the washer outlet near the sink.
Similar Threads: Proximity washer
Electrical Forum discussion & Blog electrical supply proximity to propane line? Feb 26, 2008
Electrical Forum discussion & Blog Dishwasher wiring all of a sudden overheats and melts Feb 27, 2017
Electrical Forum discussion & Blog Dishwasher bad luck, or electrical? Feb 16, 2015
Electrical Forum discussion & Blog Need branch ckt diagram for instllation of washer/dryer for permitting Dec 14, 2014
Electrical Forum discussion & Blog Help new washer timer wires not matching up Jun 28, 2013