proper way to plumb a tempering valve?

Users who are viewing this thread

northman

Member
Messages
35
Reaction score
0
Points
6
Location
Washington
Hello all, I am going to install a tempering valve at the hot water heater. Is it better to T off the cold pipe to the tempering valve before or after the cold water shutoff valve?

I'm thinking one way is better, and of course the other is easier, just like a little reinforcement before I make a choice.

Thanks for the help.


Greg
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
If you Teed in before the cutoff, then if you wanted to shut off hot water in order to work on some fixture, you would still have the possibility of cold water coming through the tempering valve to the hot side. Depending on what type of facility this is installed at, this may or may not be a major issue.
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
valve

I had a customer who could not get a proper flow of hot water. His circulating line was connected before the heater's valve, and someone had shut off the valve, so sold water was flowing through the system backwards. Your tempering valve will do the same thing if it is connected before the valve, so you would have to add a shutoff valve to it, in order to service the water heater or hot water system.
 

northman

Member
Messages
35
Reaction score
0
Points
6
Location
Washington
jimbo said:
If you Teed in before the cutoff, then if you wanted to shut off hot water in order to work on some fixture, you would still have the possibility of cold water coming through the tempering valve to the hot side. Depending on what type of facility this is installed at, this may or may not be a major issue.

I know, I think the easier solution is to add a 2nd valve at the tempering valve, not quite elegant, but functional.
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
valve

Functional? yes. Inelegant? Yes. A nuisance? Yes, because you have to remember to shut off two valves. Why not do it correctly and connect after the heater's valve?
 

CHH

New Member
Messages
224
Reaction score
0
Points
0
Location
Denver, CO
hj said:
Functional? yes. Inelegant? Yes. A nuisance? Yes, because you have to remember to shut off two valves. Why not do it correctly and connect after the heater's valve?

An isolation valve for the tempering valve should still be used. If isolation is not available, what do ya do when the tempering valve fails? Wait on a plumber or trip to the supply store? No, just close a valve, lower an aquastat and the system is back in business until repairs can be made.
 

northman

Member
Messages
35
Reaction score
0
Points
6
Location
Washington
CHH said:
An isolation valve for the tempering valve should still be used. If isolation is not available, what do ya do when the tempering valve fails? Wait on a plumber or trip to the supply store? No, just close a valve, lower an aquastat and the system is back in business until repairs can be made.

Good point, although the tempering valve I have is Italian, no worries there, right?

2nd valve is sounding better.
 

CHH

New Member
Messages
224
Reaction score
0
Points
0
Location
Denver, CO
northman said:
Good point, although the tempering valve I have is Italian, no worries there, right?

Should be fine with a nice Chianti...:)
 