Proper Size Gas Pipe to Dryer?

Users who are viewing this thread

Statjunk

DIY Senior Member
Messages
540
Reaction score
0
Points
0
Hello All,

It's been a while since I've been on here. I hope that most everyone is still on here. Feels like it's been a year or so since I've been on here. In that time I've gotten married, had a son, folded my contracting business, got laid off from my day job, found another day job wheeeee. Just writing that makes me tired.

The issue I'm dealing with here is I have a dryer sitution. I don't believe the dryer is getting enough gas to heat. It takes three hours to dry a load. Surprising it took me two dryers to actually check the gas line. Turns out someone ran 3/8" OD soft copper from the attic down to the dryer. So that means it's 1/4" ID.

Total run length is 8-10 feet and junctions from a 3/4" to 1/2" black pipe "T".

It's in a very tight spot in the attic and can't be gotten from below because of existing cabinetry. So I want to use soft pipe.

Would 1/2" OD soft copper be sufficient to run a dryer?

How about if coming off the T are two 1/2" S. 90's in order to line it up. Essentially I'm using the 90's to keep the soft copper below the joists. Otherwise it will have to be above an susceptible to damage.

Thanks

Tom
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
Slow dry time is ALMOST always caused by a blocked exhaust duct. In your case, it might actually be the gas line. 1/4" ID is pretty small . 30 feet of that supports only about 10,000 BTU and I suspect a dryer is a lot more than that. For 1/2" ID, 30 feet supports about 47,000 BTU/

gas_sizing_chart.jpg
 
Last edited by a moderator:

Statjunk

DIY Senior Member
Messages
540
Reaction score
0
Points
0
Hey Jimbo,

Any idea what 3/8" ID supports? It's a 10' run.

Thanks

Tom
 

hj

Master Plumber
Messages
33,599
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
Gas lines often "support" more btus than the charts list, because the burners will still operate at less pressure than the charts assume, but 3/8" copper might be too small. Have you looked at the burner flame while the dryer is operating?
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
Hey Jimbo,

Any idea what 3/8" ID supports? It's a 10' run.

Thanks

Tom

3/8 ID at 10 feet is listed at 420000 BTU. That is why it is usually OK to use a 3/8 ID 3 foot long flex gas connector for dryers.

I get these figures from the National Fuel Gas Code charts, also found in the CA Plumbing Code book. I use the chart for copper, less than 2.0 PSIG, 0.3" wc drop. There is a slightly less conservative chart for 0.5" wc drop.
 

Statjunk

DIY Senior Member
Messages
540
Reaction score
0
Points
0
Thanks guys. I really appreciate the info. The dryer states on it that it's 22,500 BTU. So a 10' run of 1/2" OD - 3/8" ID should do the trick. Anyone care to guess what I'll be doing this weekend?

Tom
 

Gator37

Retired prof. engr.
Messages
108
Reaction score
0
Points
0
Location
Alabama
Jimbo is correct. One source is NFPA 54 for pipe sizing charts.
 