Proper settings Enertrol

Discussion in 'Boiler Forum' started by GregoryR, Oct 22, 2011.

  1. GregoryR

    GregoryR New Member

    Messages:
    21
    Location:
    Maine, USA
    Hello,

    Could any of you help me with setting this thing (outdoor reset) up properly? People on this site were a real good help last time I had questions, and I thank all of you for your time.

    [​IMG]
  2. Tom Sawyer

    Tom Sawyer In the Trades

    Messages:
    3,167
    Location:
    Maine
    I would need to know which model you have or a photo
  3. GregoryR

    GregoryR New Member

    Messages:
    21
    Location:
    Maine, USA
    [​IMG]

    Uploaded with ImageShack.us

    I had tried to upload one earlier, but I think it was too large. This should work.
  4. Tom Sawyer

    Tom Sawyer In the Trades

    Messages:
    3,167
    Location:
    Maine
    Set the slide switch to mod and turn the dial to 160 to start. You're up here in Maine with me so, when it gets damn cold out, if the house won't heat, turn the dial up 20 degrees until it will. You can also try going lower if the house is heating ok. The dial is what sets the temperature differential between outside temp and boiler supply temp, adjusted for degree days. I found that 160 to 180 seems to work pretty good around here.
  5. GregoryR

    GregoryR New Member

    Messages:
    21
    Location:
    Maine, USA

    Done and done, thanks so much. Hopefully we'll see some savings now that this thing is actually doing its job.
Similar Threads: Proper settings
Forum Title Date
Boiler Forum Sizing new Boiler properly (methodology) - mid atlantic Maryland Mar 21, 2013
Boiler Forum peerless combi 160 gas boiler circulator not controlling properly Oct 10, 2012
Boiler Forum Properly venting a Wei-McLain CGi-4E boiler into a flue? Jan 28, 2010
Boiler Forum Aquastat settings Dec 24, 2013
Boiler Forum Oil burner with Enertrol HWDT-R-S Settings Mar 16, 2013

Share This Page