So you say the PRV is to protect the bladder.... And here I always thought the PRV was to prevent the pressure tank from exploding, or to prevent the pump from being blown off PE pipe etc. etc., not to protect the bladder... but tell us why that would be since the tank, and I assume the bladder, has a 120-125 psi working pressure or do I have that wrong?
 

Sammyhydro11

In the Trades
Messages
708
Reaction score
1
Points
16
Location
Massachusetts
The relief valve will protect the diaphragm and other components.The tank is tested at 125psi. Amtrol says the relief valve should be set at 75psi should be installed with their residential tanks. This setting will protect the tanks components as well as fittings.
I have always installed the proper relief valves recommended by the manufacturer. My settings on the tanks as well. If you always do things the right way, you will never have problems. I have never really went into figuring out what the actual pressure on a diaphragm was and i will admit, it's cool that Witch pointed it out. I will tell you this, assuming someone doesn't know simple math because i didn't point out the actual pressure on a diaphragm is ridiculous. I simply pointed out what the settings should be. The only thing that was missing on my part, was if the correct settings are off then the diaphragm could be damaged.

I have no problem admitting that i am wrong about something, when i am. I most certainly don't appreciate the whole comment on education.

sammy

www.tylerwellandpump.com
 

Gary Slusser

That's all folks!
Messages
6,921
Reaction score
22
Points
38
Location
Wherever I park the motorhome.
Website
www.qualitywaterassociates.com
Then like I said, at 75 psi they are protecting the tank from explosion like the T/P valve on a water heater, not the bladder. And I think if you look close, there will be a sticker on the tank stating the max operating/working pressure because the PRV isn't code everywhere. And yes, I always installed one whether the customer wanted it or not, there was no option.

The education thing. Do unto others as you...
 

42skidoo

New Member
Messages
23
Reaction score
0
Points
0
Relief valve

The system is working however I have a cistern pump that is running too. The well pump fills the pressure tank and shuts off at 58 psi as indictaed by the gauge. Then the cistern pump kicks on and jacks the pressure up to 60 and the relief valve pops. Are my pressure switch settings wrong?
 

Gary Slusser

That's all folks!
Messages
6,921
Reaction score
22
Points
38
Location
Wherever I park the motorhome.
Website
www.qualitywaterassociates.com
You should check the air pressure in both bladder tanks and adjust it to be 1-2 psi less than the turn the pump on setting on the switches. I.E. 30on/50off gets 29-28 psi air pressure with no water in the tank.

If you have old water pressure gauges you might want to replace them. And use a good air gauge.

Then if the PRV still leaks then it's probably bad or has dirt in it preventing it from sealing closed.
 

42skidoo

New Member
Messages
23
Reaction score
0
Points
0
Time to call in the troops

After countless hrs I finally called in the well experts. The consensus is this: I have a well pump and a cistern pump. The well pump is activated via the pressure switch. The cistern pump is activated via a float switch. The cistern shuts off when the float rises and is not tied to my pressure switch. My problem was I couldnt figure out why my safety switch (to prevent well pump running dry) kept tripping. Turns out the safety switch is working fine and the well is only producing about 1/2 gallon of water per hour. Needless to say this is not good. We adjusted the safety switch to turn off sooner just to protect the pump, is that's even possible.
 

42skidoo

New Member
Messages
23
Reaction score
0
Points
0
Time to call in the troops

The well pump is indeed running off the pressure switch. Turns out the safety switch kept tripping and shutting down the well pump because there is not enough water ie 1/2 gallon an hour. I thought there must be something
wrong in the wiring but indeed this was the case.
 

Masterpumpman

In the Trades
Messages
729
Reaction score
1
Points
0
Location
Virginia Beach, VA
Website
www.dci-inc.us
Graduate from High School?

High School has nothing to do with knowledge! I knew a Harold McGee of Kerr-McGee Oil Corporation that never went to High School however he was self taught and was one of the smartest men I have ever met.
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks