Prioritized IHW Cycling

Discussion in 'Boiler Forum' started by mage182, Apr 24, 2012.

  1. mage182

    mage182 Member

    Messages:
    69
    Location:
    NY
    I have a Burnham Alpine 150 with a Burnham 50 gal IHW tank piped off of the secondary loop using 1" copper. The tank has priority. My question is should I be tweaking the max fan speed on calls for hot water so that the boiler only cycles once for as long as needed each time the tank calls for hot water? Or is this a moving target? The boiler doesn't cycle more than once every time the tank calls for water, but it does happen sometimes.

    The max fan speed on the boiler is 5500 and I believe that the max it is set to right now for hot water calls is 4000. This number can be set independently from the max fan speed when heating zones are calling for heat.
  2. Dana

    Dana In the trades

    Messages:
    2,930
    Location:
    01609
    It probably doesn't much matter if the minimum burn time during hot water calls is at least a couple of minutes. If the boiler is only getting ahead of the heat exchanger once in awhile it's not a big deal. If it were happening often or every time, it's worth dialing back the flow or taking other measures on the primary side to prevent it.

    If it's simply a matter of punching in a number into the setup on this boiler, go ahead. As long as you're not running out of hot water, the lower the firing rate the better. Running the boiler at a lower fire modestly improves the combustion efficiency of a mod con.
Similar Threads: Prioritized Cycling
Forum Title Date
Boiler Forum Too much cycling Sep 30, 2012
Boiler Forum Need help with cycling issue- Monitor MZ25S Boiler Oct 25, 2011
Boiler Forum Short-cycling boiler Jul 20, 2011
Boiler Forum Help ASAP: Short cycling Oct 24, 2010
Boiler Forum Purefire Pinnacle 140 short cycling with Boost Jan 3, 2010

Share This Page