Pressure testing a new loop before connecting

Discussion in 'Boiler Forum' started by nh.hiker, Nov 29, 2011.

  1. nh.hiker

    nh.hiker New Member

    Nov 29, 2011
    I've just finished a lengthy basement renovation that involved replacing the old base board with shiny new Slant Fin. Prior to the remodel, the basement and first floor where on the same thermostat which made the basement pretty warm when the first floor was comfortable. So I wanted it on its own zone.

    During the remodel, I had the boiler replaced (System2000) and they piped in stubs and a zone valve for the basement loop. I'm finished now and wanted to pressure test the loop before connecting back to the boiler.

    I don't have a gauge that I can solder in. I've got the material to cap one end and put a valve stem on the other. I'll need need to use a tire pressure gauge.

    My question is, how much pressure to use and how long do I need to test?

    Thanks for the help
  2. BadgerBoilerMN

    BadgerBoilerMN Hydronic Heating Designer

    Mar 4, 2011
    hydronic heating designer/contractor
    Every manufacturer of PEX tubing specifies an air or water test, they range from 30 to 100lbs/ and the test may last five minutes to 24 hours, you should use the manufacturer's spec but for my radiant floor heating installations here in Minneapolis I generally use 60#/24hrs. or 100#/15 minutes. Please do not leave 100# pressure on the system while pouring cement or gypsum based products or in any case leave the high pressure test unattended.
  3. Sponsor

    Sponsor Paid Advertisement

Similar Threads: Pressure testing
Forum Title Date
Boiler Forum Alpine boiler losing pressure when isloated Thursday at 9:03 AM
Boiler Forum Boiler pressure problem Apr 23, 2015
Boiler Forum Burnham v8 - Fluctuating pressure Mar 13, 2015
Boiler Forum pressuretrol tripped? Jan 28, 2015
Boiler Forum GB 142 24/45 pressure relief valve. Jan 21, 2015

Share This Page