  1. fdesantis

    fdesantis New Member

    Joined:
    Feb 25, 2005
    I have a 13 year old SquareD pumptrol type FSG2 pressure switch which recently started exceeding the cut out setting. I believe it was previously set at 40/60. Last night I discovered water leaking from the check valve. It appears that the switch isn't recognizing the increase in pressure properly and is now shutting off around 80+ psi. It does however cut in properly at 40 psi. I've tried adjusting the differential with little to no success. From what I've read here, it seems that either it's time to replace the switch or possibly the inlet to the switch may be clogged. My well guy can't come until next week and I'd rather not wait. So instead of calling around for other people, I'm considering doing it myself. For those who have replaced a switch before, on a scale of 1 to 10 (with one being easy) how would you rate this job? I consider myself pretty handy and have done other plumbing (no soldering skills though) and electrical projects. I'd appreciate any advice or information on things to watch out for. Thanks in advance.
     
  2. Hube

    Hube New Member

    Joined:
    Sep 1, 2004
    Location:
    Ontario
    Replacing an existing switch presents no problem at all, especially if using the same type, etc. Imo, a scale of an easy 2... :)
    Note; make sure the tube to the switch is clean of any goop/crud.

    Most Square D sfg2 switches are set at 20/40 or 30/50. So make sure you follow the instructions on raising the settings.

    Also, make sure the pressure tank (when empty ) has air pressure set at 2 psi below the pump's cut-in setting.

    Good luck...Hube
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. fdesantis

    fdesantis New Member

    Joined:
    Feb 25, 2005
    Replacing the switch turned out to be pretty easy and everything seems to be working fine now. Thanks.
     
  5. Deb

    Deb Plumber

    Joined:
    Sep 5, 2004
    Location:
    Idaho
    Deb

    It is always a good idea to check and/or replace the nipple, too. These are a narrow diameter and can clog easily, giving a false pressure reading to the switch.
    Deb
    The Pipewench
     
Similar Threads: Pressure Switch
Forum Title Date
Pumps and Tanks Well Forum & Blog Pressure switch contacts closed, power both sides, pump not running Tuesday at 1:37 PM
Pumps and Tanks Well Forum & Blog Low pressure switch Monday at 3:17 PM
Pumps and Tanks Well Forum & Blog pump/pressure switch Feb 6, 2015
Pumps and Tanks Well Forum & Blog Pressure on pump keeps going up, up, and up. Bad pressure switch? Jan 19, 2015
Pumps and Tanks Well Forum & Blog Bouncing pressure switch Nov 23, 2014

Share This Page