I don't believe there is one, but just checking to be sure. Is there a maximum length a drain pipe can be run from the water heater pressure relief ?

This pipe is running to the exterior of the building, and the total length is 27 ft. from the water heater. other than that its ok.
 

Dj2

In the Trades
Messages
2,611
Reaction score
258
Points
83
Location
California
In many places it's code to run it (in metal pipe) to the exterior, 6" above grade.
As long as you maintain 1/4" drop every foot in length, the distance can be 27 feet.
 