    I have a Bradford White MI TW 50 gl power vent tank.
    Blower was making noise and had come apart. Replaced blower assy with factory parts.
    Plugged in and ran fine. After tank was hot, blower would not shut off. Blower runs even though the burner is not on. 2" PVC vent pipe is not hot to the touch.
    Any Ideas??
  2. Dana
    Dana In the trades
    Jan 14, 2009
    01609
    Assuming (in lieu of evidence) that you wired it correctly, that would imply that the relay the powers the blower is stuck on (contacts welded, spring broken, something) or something even further back the control chain is fried.
    In the meantime just letting it run is not a good option, since it's sucking heat out of the tank 24/7, blowing it out the vent.
  4. rexles
    rexles New Member
    Jul 27, 2010
    Holland, OH
    Wiring was simple plug that could only be plugged in one way.
    It seems the diaphram switch was not being pulled in when blower was running. I removed the blower and remounted it using silicone to seal around the base where it sets on the HW tank. One of the sheet metal screw holes was stripped out so I installed bigger screws. Plugged it in and it fired right up.
    Evidently the lack of a good seal was enough to make the vacuum on the diaphram switch not pull in. The blower is controlled by the thermostat, and the gas valve is controlled by the vacuum switch on the blower unit.
  5. ballvalve
    Dec 28, 2009
    northfork, california
    Those air switches are very sensitive, when the diaphragm gets harder with age, the required vacuum climbs, and it still works when you 'suck on it'.
    Odd, however, because if the diaphragm switch does not close, you shouldnt get gas to the valve, and the blower should power down.
    Sequence-call for heat- blower starts- air switch senses vacuum from blower- igniter on- blower on. gas valve opens.
  6. rexles
    rexles New Member
    Jul 27, 2010
    Holland, OH
    You are correct on your sequence, however the blower is controlled by the thermostat and does not shut off until satisfied. The vacuum switch pulls in the gas valve and even if the gas valve does not open the blower continues to run. Tech at BW told me that over the phone and it was also proven true by standing there and watching it.
  7. Master Plumber Mark
    Master Plumber Mark Master Plumber
    Feb 6, 2005
    Sensitivity trainer...healey-feeley.....
    shut it down
    you would be wise to check the air switch, thermostat, relay
    that tells the unit to shut off...
    and whatever else they tell you could be the trouble...
    the blower will run till it burns out, and it will certainly
    cool down the heater and make it come on and re-heat...
    costing you money....
    shut it down, take it apart again and start over...
  8. rexles
    rexles New Member
    Jul 27, 2010
    Holland, OH
    Evidently you failed to read my post correctly. It was fixed when I pulled off the blower assy and sealed it with silicone and screwed it down again with abigger screw that had stripped out. It is running the way it should.
  9. ballvalve
    Dec 28, 2009
    all the rigs I see shut off the blower if the vacuum switch does not pull in.
  10. Master Plumber Mark
    Feb 6, 2005
    I am so very sorry sherlock...... how silly of me old chap.....
    evidently , these other two guys did not read your
    post very well either.....
    please stick your snooty nose up in the air for them too,
    whould you please.
Similar Threads: Power vent
Water Heater Forum, Tanks Power Vent Water Heater Venting Jan 13, 2017
Water Heater Forum, Tanks Direct vented vs power vented water heaters Jun 8, 2016
Water Heater Forum, Tanks Power vent, efficient motor? Feb 2, 2016
Water Heater Forum, Tanks Time to replace or what ?? LP power vent water heater Jan 27, 2016
Water Heater Forum, Tanks GE Powervent GG50S06RVK Water Heater help? Sep 14, 2015