Portable Generator Grounding

Discussion in 'Electrical Forum discussion & Blog' started by jdavis1137, Nov 3, 2007.

  1. jdavis1137

    jdavis1137 New Member

    Messages:
    1
    I just purchased a Coleman Powermate portable generator,(5700 watts) for backup power for power outages. I also had a licensed electrician install a Emergen manual transfer switch to my existing house panel. The generator will be attached to the transfer switch with a Emergen power cord, 4 wire , 30 amp, L14-30 NEMA configuration. The generator instructions says something about grounding the generator. Isn't everthing already grounded thru the installation that the electrician did wiring up the transfer switch to my existing panel? It would be a major job to drive a 8 foot copper pole in the ground and attach a 12g grounding wire, as there is nothing close to ground to where my generator has to be located. I would really appreciate some information on this grounding situation as I want to be ready before the next storm. Thank you
  2. Chris75

    Chris75 Electrician

    Messages:
    608
    Location:
    Litchfield, CT
    You do not need a ground rod if your generator is not a SDS, (Separately Derived System) In order to know this, see if the neutral is switched in the transfer switch... (Highly Doubtful)
  3. jwelectric

    jwelectric Electrical Contractor/Instructor

    Messages:
    2,542
    Location:
    North Carolina
    I agree with Chris and will add;

    If the grounded (neutral) conductor is not switched in the transfer switch then the bonding jumper in the generator will need to be remved.
Similar Threads: Portable Generator
Forum Title Date
Electrical Forum discussion & Blog Generac Portable Generator Nov 2, 2011
Electrical Forum discussion & Blog Is this portable generator hook-up OK? Oct 20, 2011
Electrical Forum discussion & Blog using coleman ground fault extention cord with portable generator Feb 24, 2011
Electrical Forum discussion & Blog Connecting a portable generator to home main panel May 19, 2010
Electrical Forum discussion & Blog Portable generator and generator panel incompatibility May 12, 2009

Share This Page