plumbing over electric panel

Discussion in 'Plumbing Forum, Professional & DIY Advice' started by Zenman, Sep 12, 2009.

  1. Zenman

    Zenman New Member

    Joined:
    Nov 26, 2004
    Location:
    New Jersey
    Is there a restriction on how close the water supply lines can be to the electric service panel? Currently the water supply runs directly above the main panel and I'm doing some renovations and have to move the supply line. So when I replace the line, is there some minimum distance that I need to maintain?
     
  2. FloridaOrange

    FloridaOrange Plumbing Designer

    Joined:
    Dec 2, 2005
    Occupation:
    Plumbing Designer
    Location:
    SW Florida
    I never put water piping or ductwork directly over panels. Use some common sense and you should be fine.
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. hj

    hj Moderator & Master Plumber Staff Member

    Joined:
    Aug 31, 2004
    Occupation:
    Plumber
    Location:
    Cave Creek, Arizona
    water

    Spacing requirements have to do with possible contact with the piping while working in the panel. If the pipes are overhead there would be little reason to make contact with them.
     
  5. Cass

    Cass Plumber

    Joined:
    Nov 12, 2005
    Location:
    Ohio
    What was the distance and what do you want it to be...
     
  6. Zenman

    Zenman New Member

    Joined:
    Nov 26, 2004
    Location:
    New Jersey
    Thanks for the replies so far...

    This is in the basement. The panel is against the wall and the supply is 6 inches above the top of the panel and 12 inches in front of it. I was going move it over at least one joist bay (16 inches + the original 12 inches = 28 inches in front of the panel, and still 6 inches above). I could move it an additional joist bay over if necessary.
     
    Last edited: Sep 12, 2009
  7. jar546

    jar546 In the Trades

    Joined:
    Feb 20, 2008
    Location:
    USA
    E3305.3 Dedicated panelboard space. The space equal to the
    width and depth of the panelboard and extending from the floor
    to a height of 6 feet (1829 mm) above the panelboard, or to the
    structural ceiling, whichever is lower, shall be dedicated to the
    electrical installation. Piping, ducts, leak protection apparatus
    and other equipment foreign to the electrical installation shall
    not be installed in such dedicated space.
    The area above the dedicated
    space shall be permitted to contain foreign systems, provided
    that protection is installed to avoid damage to the electrical
    equipment from condensation, leaks and breaks in such foreign
    systems (see Figure E3305.1).
    Exception: Suspended ceilings with removable panels shall
    be permitted within the 6-foot (1.8 m) dedicated space
     
  8. nhmaster

    nhmaster Master Plumber

    Joined:
    Jul 30, 2008
    Occupation:
    Tech. Instructor
    Location:
    S. Maine
    Yea Jar that's it, that's it exactly :D
     
  9. Zenman

    Zenman New Member

    Joined:
    Nov 26, 2004
    Location:
    New Jersey
    OK... from that it seems that no supply lines directly above the panel are allowed. It doesn't specify a distance in front of the the panel, so I guess as long there is some separation I should be good. I was going to be at least 28 inches in front of the panel (if not more), AND above 6 feet, so I shouldn't have a problem.

    Thanks!
     
    Last edited: Sep 12, 2009
  10. FloridaOrange

    FloridaOrange Plumbing Designer

    Joined:
    Dec 2, 2005
    Occupation:
    Plumbing Designer
    Location:
    SW Florida
    Correct, the issue code wise is leaking *and sweating from HVAC* down onto the panel or feeders.
     
Similar Threads: plumbing electric
Forum Title Date
Plumbing Forum, Professional & DIY Advice Is there a plumbing equivalent to Richter's "Practical Electrical Wiring" book? May 5, 2010
Plumbing Forum, Professional & DIY Advice Question - Plumbing/Electrical Nov 3, 2009
Plumbing Forum, Professional & DIY Advice plumbing and electrical Nov 2, 2008
Plumbing Forum, Professional & DIY Advice Electrical/ plumbing in same stud bay Feb 8, 2008
Plumbing Forum, Professional & DIY Advice Does this cast iron look okay to use for two floors of home plumbing? Thursday at 5:41 PM

Share This Page