Please review the piping plan for basement remodel

Discussion in 'Plumbing Forum, Professional & DIY Advice, Tips & ' started by Miles to Go, Jun 21, 2013.

  1. Miles to Go

    Miles to Go New Member

    Messages:
    1
    Location:
    Baltimore, MD
    Hey everyone, we’re starting to remodel a basement in our house that is 90+ years old. We’ve read many, many, many posts on this forum, hoping to educate ourselves.

    The existing 3†soil pipe is above ground where we want to put the new bathroom (which is below the first floor bathroom). It does enter the ground across the room.

    To avoid using a swage ejection pump, we are planning to trench across the basement until we meet the existing soil pipe under grade. We’ll probably have to use 1/8th inch over 12†pitch to meet up with the existing soil pipe. The new 3†pipe will be approximately 30 feet long, and will meet the existing soil pipe which is 4.5†below grade.

    The new basement toilet, lavatory, shower, and washing machine will drain to this new pipe, and the vents will connect to the existing vent that the first floor bathroom uses. I have the shower and the washing machine sharing a vent, not sure if that is allowed.

    Can you please review the piping plan for any glaring mistakes? (see 5 images below). Please assume that all drain pipes will be pitched at ¼ inch over 12â€, and the vents will be pitched so that they will drain back to the drain they are venting. (Modeling the pitch was very difficult, so I gave up on it!). You’ll see several wye’s that are on their sides, assume they will be canted upwards to gain the required pitch. (Again difficult to model). PLUMBING.jpg PLUMBING iso1.jpg PLUMBING iso2.jpg EXISTING1.jpg EXISTING2.jpg
  2. hj

    hj Moderator & Master Plumber Staff Member

    Messages:
    26,488
    Location:
    Cave Creek, Arizona
    pipe

    What difference does it make whether the pipe is 40 or 45 degrees as far as the depth is concerned. IF the pipe is NOT at a 45 degree angle, your other fittings will not line up properly. If the sewer is only 4 1/2" deep, it is too shallow to make the connection to the toilet. You are connecting to a DRAIN line, not a vent by the tub and can absolutely NOT DO THAT, and the downstairs shower is not vented.
    Last edited: Jun 21, 2013
  3. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Messages:
    21,896
    Location:
    New England
    If the drain line was 4", you might be allowed to use 1/8"/foot. Sounds like you need an ejection pump, UNLESS, you can run the line outside the foundation and find a place low enough that will allow you to provide the needed slope. This might be a good ways towards where the existing sewer line meets the main for the neighborhood. This is typically below the frost line, and could be much deeper than that.
Similar Threads: Please review
Forum Title Date
Plumbing Forum, Professional & DIY Advice, Tips & Please review my plan for bath plumbing Aug 9, 2014
Plumbing Forum, Professional & DIY Advice, Tips & Help with DWV layout for new bathroom - please review layout Dec 9, 2013
Plumbing Forum, Professional & DIY Advice, Tips & Please review my DWV layout Aug 8, 2013
Plumbing Forum, Professional & DIY Advice, Tips & Please review this drain rough Apr 9, 2013
Plumbing Forum, Professional & DIY Advice, Tips & Review Shower DWV Diagram Please - ready to install Nov 26, 2012

Share This Page