    I have chosen this style of radiator for my home and I'm trying to figure out the right one for each room.

    Does any one know how to convert the displayed numbers into a BTU output?

    [​IMG]


    [​IMG]

    JW - "When it's perfect. It's Good Enough."

    www.No-Curb.com - my blog site on Barrier Free, No Curb, No Dam and Hobless Showers
    (604) 506-6792 jfrwhipple@gmail.com
     

    Attached Files:

    Last edited: Jan 10, 2015
  2. frenchie

    frenchie Jack of all trades

    Joined:
    Dec 30, 2006
    Occupation:
    Caretaker
    Location:
    Brooklyn, NY and Fire Island, NY
    [​IMG]


    Note for hot water, the above chart says "AVERAGE water temperature" - midway between supply water temp & return water temp - NOT "supply water temperature".
     
    Last edited: Dec 31, 2009
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. Doherty Plumbing

    Doherty Plumbing Journeyman & Gas Fitter

    Joined:
    Jun 22, 2009
    Occupation:
    Red Seal Journeyman Plumber & Licensed Gas Fitter
    Location:
    Penticton, BC

    The heat loss across those rads would be entirely dependent on the system you have installed. IE the flow rates and working temps of the water.
     
  5. Scuba_Dave

    Scuba_Dave Extreme DIY Homeowner

    Joined:
    Jan 5, 2009
    Occupation:
    Used to be in IT
    Location:
    South of Boston, MA
    One of the TV shows did a special on CI radiatiors & I picked out the ones I wanted
    Turns out the company is in the UK & does not have a distributor in the US, & no plans for one
    They were flooded with E-mails asking how to buy their product
    They had no idea they were being featured on the TV show

    I'll be buying some other ones in the US, maybe used


    [​IMG]
     
  6. johnfrwhipple

    johnfrwhipple BATHROOM DESIGN & BUILD for both Canada & the US

    Joined:
    Jul 20, 2009
    Occupation:
    Design Work World Wide: Bathrooms Vancouver Area
    Location:
    North Vancouver, BC
    Calculating total BTU output for the radiators

    Thanks for the information guys.

    The chart is excellent - I can get a pretty good idea of the size now for each room and will leave the exact measurements for my engineer.

    Happy New Years,

    Again thanks for the help.


    JW - "When it's perfect. It's Good Enough."

    www.No-Curb.com - my blog site on Barrier Free, No Curb, No Dam and Hobless Showers
    (604) 506-6792 jfrwhipple@gmail.com
     
    Last edited: Jan 4, 2015
  7. nhmaster

    nhmaster Master Plumber

    Joined:
    Jul 30, 2008
    Occupation:
    Tech. Instructor
    Location:
    S. Maine
    you can't go wrong over sizing a radiator either. the extra size means you can lower water temperatures.
     
  8. johnfrwhipple

    johnfrwhipple BATHROOM DESIGN & BUILD for both Canada & the US

    Joined:
    Jul 20, 2009
    Occupation:
    Design Work World Wide: Bathrooms Vancouver Area
    Location:
    North Vancouver, BC
    Heat loss from building a window seat over standard baseboard heat

    I have read online that just painting the radiators cause a decrease in heat output. This can be a blessing or a nightmare I'm sure.

    If I had a standard baseboard heater with the copper pipe and fins (with cover) what do you think the percentage of heat loss would be if I built a window seat above the unit to conceal it. My ballpark guess is 30% do any of you HVAC specialist think this guess is way off?


    JW - "When it's perfect. It's Good Enough."

    www.No-Curb.com - my blog site on Barrier Free, No Curb, No Dam and Hobless Showers
    (604) 506-6792 jfrwhipple@gmail.com
     
    Last edited: Jan 4, 2015
  9. johnfrwhipple

    johnfrwhipple BATHROOM DESIGN & BUILD for both Canada & the US

    Joined:
    Jul 20, 2009
    Occupation:
    Design Work World Wide: Bathrooms Vancouver Area
    Location:
    North Vancouver, BC
    Working on the BTU output for a 3 column radiator

    Working off the Standing Radiator Heat Emission table above and the information from Burnham I came up with these calculations.

    A 3 column cast iron radiator (as shown above) 32" tall x 4 3/4" deep x 25" wide totals 32 1/2 square feet. With a water temperature of 170 degrees Fahrenheit the chart show I get 150 BTU's per hour per square foot.

    I have checked my math and this works out to the above unit producing 4875 BTU's per hour. This is fantastic as the standard base boards that are cheap and easy are only producing about 760 BTU's for the same foot print (2' linear feet).

    I will send my specs to Burnham and they do all this calculating for me. I am trying to use as many of the cheap baseboards as possible and make up the missing heat with the column radiators.

    If I have them painted white which I most surely do the heat output will be affected as I have read. Even if the painting drops this number by 10-20% the unit is still cranking out huge heat in a small area!


    JW - "When it's perfect. It's Good Enough."

    www.No-Curb.com - my blog site on Barrier Free, No Curb, No Dam and Hobless Showers
    (604) 506-6792 jfrwhipple@gmail.com
     
    Last edited: Jan 4, 2015
  10. Scuba_Dave

    Scuba_Dave Extreme DIY Homeowner

    Joined:
    Jan 5, 2009
    Occupation:
    Used to be in IT
    Location:
    South of Boston, MA
    I recently repainted 3 CI radiators in our house
    Possibly only the 2nd time they were painted - house from the 50's
    Very little paint on them, a lot worn off
    At the same time I turned the boiler Temp down ~20 degrees
    Our house has always been warm since renovations/new windows & insulation

    I'm sure it retains some heat, doubt I could tell
    I do know it takes slightly longer for the house to heat up (due to lower temp)
    And the heat will come on again sooner
    But the Temp was too high IMO @190 - with a 2.5 year old in the house
    Our boiler is oversized, & the kitchen radiator is huge as the stairs to 2nd floor are off the kitchen

    Our 864 sq ft addition I am going to use CI radiators
    I'd rather spend the extra $$ & have them instead of slant fins along a lot of the walls
     
    Last edited: Jan 1, 2010
  11. johnfrwhipple

    johnfrwhipple BATHROOM DESIGN & BUILD for both Canada & the US

    Joined:
    Jul 20, 2009
    Occupation:
    Design Work World Wide: Bathrooms Vancouver Area
    Location:
    North Vancouver, BC
    Cast Iron radiators for looks

    I agree they look great.

    Since we made our decision to use them we see them every where now. TV, Books and movies.

    Many of our design magazines that we flip through for ideas have them as well which we really didn't notice a few years back when we started collecting them.

    Some awesome looking Rad's right here: Available in Canada and the US by Hudson Reed.


    Neo Classic by Hudson Reed USA
    [​IMG]
    I love the patina of this one!




    JW - "When it's perfect. It's Good Enough."

    www.No-Curb.com - my blog site on Barrier Free, No Curb, No Dam and Hobless Showers
    (604) 506-6792 jfrwhipple@gmail.com
     
    Last edited: Jan 5, 2015
  12. Ian Gills

    Ian Gills Senior Robin Hood Guy

    Joined:
    Jul 24, 2007
    Occupation:
    Robber, with some DIY on the side.
    Location:
    USA
    In the more civilized parts of the world, we use these.

    [​IMG]

    Not all this bulky cast iron stuff that looks like it came out of the middle of the last century.
     
  13. frenchie

    frenchie Jack of all trades

    Joined:
    Dec 30, 2006
    Occupation:
    Caretaker
    Location:
    Brooklyn, NY and Fire Island, NY
    Yeah, it's only with toilets, that you guys prefer to use antiques.
     
  14. Scuba_Dave

    Scuba_Dave Extreme DIY Homeowner

    Joined:
    Jan 5, 2009
    Occupation:
    Used to be in IT
    Location:
    South of Boston, MA
    Sorry....but that's butt ugly to me :D
     
  15. johnfrwhipple

    johnfrwhipple BATHROOM DESIGN & BUILD for both Canada & the US

    Joined:
    Jul 20, 2009
    Occupation:
    Design Work World Wide: Bathrooms Vancouver Area
    Location:
    North Vancouver, BC
    I have installed a few Runtal Radiators

    Those Runtal style radiators work and look great - just not the look we are after.

    [​IMG]
    Rundal Radiator

    I want the home to look when finished to have just been completed in the late 30's to early 50's. The amount of contemporary radiators out on the market blows my mind. You could almost start your whole home design around which radiators you want to use.


    JW - "When it's perfect. It's Good Enough."

    www.No-Curb.com - my blog site on Barrier Free, No Curb, No Dam and Hobless Showers
    (604) 506-6792 jfrwhipple@gmail.com
     
    Last edited: Jan 5, 2015
  16. nhmaster

    nhmaster Master Plumber

    Joined:
    Jul 30, 2008
    Occupation:
    Tech. Instructor
    Location:
    S. Maine
    I have all old 6 tube CI radiators in my house. I found them at a local salvage yard. sandblasted, tested and re-fitted them, painted them to match the room colors, so some are beige, some are a light seafoam green, a couple are white, the one in the bathroom is dark tan. If I get them up to load and shoot them with my digi-temp, they all read the same.
     
  17. Scuba_Dave

    Scuba_Dave Extreme DIY Homeowner

    Joined:
    Jan 5, 2009
    Occupation:
    Used to be in IT
    Location:
    South of Boston, MA
    Some just look like wall art...but cost a lot more

    [​IMG]
     
  18. johnfrwhipple

    johnfrwhipple BATHROOM DESIGN & BUILD for both Canada & the US

    Joined:
    Jul 20, 2009
    Occupation:
    Design Work World Wide: Bathrooms Vancouver Area
    Location:
    North Vancouver, BC
    Wow. 2009 the second discussion I started here on Terry's forum.

    I did order all the Rads for my home and baseboards from the outfit back east and learned that when ordering the staff there help you size the proper rad for each room.

    My plumbing wholesaler did the heat loss calculation and after all these years my home's radiators are on of the nicest additions to the renovation!

    Took this video to showcase the bleeding valve on my Kitchen Radiator.


    Bleeding a Cast Iron Radiator


    The Learning Curve for me continues on this new discussion I started later in 2010.


    JW - "When it's perfect. It's Good Enough."

    www.No-Curb.com - my blog site on Barrier Free, No Curb, No Dam and Hobless Showers
    (604) 506-6792 jfrwhipple@gmail.com
     
    Last edited: Jan 4, 2015
Similar Threads: Picking right
Forum Title Date
HVAC Heating & Cooling Reworking Radiant Heating Zones. Does this look right to you? Sep 30, 2010
HVAC Heating & Cooling Right Filter for a Lennox 26-21-1 Furnace? Nov 29, 2009
HVAC Heating & Cooling choosing the right size modulating furnace Apr 25, 2008
HVAC Heating & Cooling How to pick right size taco pump Jun 7, 2007

Share This Page