    While you can use a regular *standard* handle ball valve with gas, why are ~gas valves~ generally have a short handle style ?

    Anyone care to shed some insight
     
  2. hj

    hj Moderator & Master Plumber Staff Member

    Joined:
    Aug 31, 2004
    Occupation:
    Plumber
    Location:
    Cave Creek, Arizona
    they are ususlly in "tight" places so as long as the handle gives enough leverage the shorter the better. And a "standard" ball valve CANNOT be used on gas, to pass an inspection, unless it also has an AGA stamping/certification.
     