I have one plumbing vent coming out of my roof by the laundry room which ties into the drain going out to the sewer. Everything else connects underground to that drain going out to the sewer…but I notice in every bathroom (under every sink) there is an AAV.

In the master bathroom, I have two sinks and they only did one AAV under one sink.

Sink 1 - No AAV

IMG_9066.jpeg


Sink 2 - AAV

IMG_9067.jpeg


Here’s a before and after (Shower, Sink 1, Sink 2, Toilet) showing how it’s all tied into the main pipe going out to the sewer. Does there need to be another AAV on the other sink? Is it okay that there’s only one AAV on Sink 2?

IMG_9069.jpeg
IMG_9070.jpeg


Any advice would be appreciated as I want to make sure my setup is correct.
 

Jeff H Young

In the Trades
Messages
8,962
Reaction score
2,237
Points
113
Location
92346
Needs a vent where Im from. but you can get by with an AAV youve got neither from what I see unless they did something inside the wall
 

wwhitney

In the Trades
Messages
6,567
Reaction score
1,847
Points
113
Location
Berkeley, CA
To amplify Jeff's comment, every trap needs a vent connection before its drain turns downward. The last picture in the OP shows the sink drains turn downward immediately inside the wall. So both sinks needs an AAV outside the wall.

Cheers, Wayne
 
Last edited:

Tuttles Revenge

In the Trades
Messages
4,205
Reaction score
1,460
Points
113
x3 that both sinks are required to have at least an AAV.

Since the bathroom is horizontal wet vented the AAV is the vent for that entire bathroom group and should be sized for the number of Drainage Fixture Units combined. It probably is, but should be verified.

Technically both of those elbows should also be long sweeps as well. Transitioning from Vertical to Horizontal and Horizontal to Horizontal require the use of long sweeps.
 

Jeff H Young

In the Trades
Messages
8,962
Reaction score
2,237
Points
113
Location
92346
Im trying to overlook things , not great work definately needs the aav but other wise mostly cosmeticaly unappealing plus disregard on those sweeps shouldnt really have issues once the vent is fixed
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks