New boiler - water pumped backwards through old system

Discussion in 'Boiler Forum' started by benj, Dec 31, 2009.

  1. benj

    benj New Member

    Messages:
    14
    Location:
    University Place, WA
    I had a new boiler installed. After the installation, I realized that the new pipes were routed such that the feed was going into the old return lines. I have an 80 year old house with 3" main feed line and 1.5" return. Now the output from the boiler goes into the prior return lines.

    I find that I keep getting air in multiple radiaters. I have to bleed some of them every two weeks for 15 minutes before the air is all out. Some just put out a little air and loose pressure. Do I have a clog secondary to displaced deposits related to the water flowing in the opposite direction?

    I find that many of the radiaters elevate to the same tempurature regardless if the valve to the radiater is on or off. I suppose that now the valve is on the outlet side of the radiaters instead of the inlet side since the water is routed backwards. Could this be the cause for the valves seemingly not working? Could the radiaters be getting hot water passively through diffusion?
    Thanks...
  2. Doherty Plumbing

    Doherty Plumbing Journeyman & Gas Fitter

    Messages:
    810
    Location:
    Penticton, BC
    So you're now pushing into the 1.5" lines and returning on the 3" line?

    You're not pushing water through the boiler backwards are you?

    You should really repipe the system to how it was before.
  3. benj

    benj New Member

    Messages:
    14
    Location:
    University Place, WA
    Yep, the feed is going into the old return lines...1.5"

    Unfortunately the water is going through the boiler the correct way (specified in the boiler manual). If it was going through the boiler and the system backwards, I would be much happier, as I could just reverse the direction of the pumps.

    I'm thinking of redoing the piping when the weather warms up. It will be a lot of work.
  4. Doherty Plumbing

    Doherty Plumbing Journeyman & Gas Fitter

    Messages:
    810
    Location:
    Penticton, BC
    Just out of curiosity.... How did one manage to pipe the supply and return backwards like that?
  5. benj

    benj New Member

    Messages:
    14
    Location:
    University Place, WA
    The company that installed the boiler realized that that they had the feed and return backwards after it was installed. I worked with them a couple days but on the last few days I had to go to work. They actually never told me about it...my dad, who was here visiting and helping out, told me that several of the installers were talking about it and didn't think it would be a problem. Unfortunately my dad didn't tell me about this until several days after the job was done. At this point, it was a little too late.
  6. johnjh2o1

    johnjh2o1 Plumbing Contractor for 49 years

    Messages:
    1,143
    Location:
    South*East
    Get them back to re pipe it. I can't see how anyone that works as a heating contractor could make such a stupid mistake.

    John
  7. benj

    benj New Member

    Messages:
    14
    Location:
    University Place, WA
    Don't know if they'll re-pipe it. I wanted to gather some evidence to support my theory that what they did is problematic. Anyone else have some ideas or have experience with this sort of situation. Any feedback would be appreciated.
Similar Threads: boiler water
Forum Title Date
Boiler Forum Sizing for a new boiler in Watertown, MA Mar 8, 2014
Boiler Forum Triangle Tube Prestige Excellence 110 Boiler - Hot Water Gives Up After 10-15 Minutes Dec 1, 2013
Boiler Forum Hot Water Lopp off Steam Boiler Suggestions Nov 20, 2013
Boiler Forum Burnham Holiday gas hot water boiler air hammer Nov 6, 2013
Boiler Forum Boiler and water shut off if leak Oct 10, 2013

Share This Page