new boiler and indirect install w/pics
Discussion in 'Boiler Forum' started by CtSebby, Dec 21, 2009.
  1. CtSebby
    CtSebby New Member
    Dec 12, 2009
    ct
    This is our first install of a boiler. does everything look ok. and comments positive or negative are welcome.
    the old beast:
    [​IMG]
    [​IMG]
    [​IMG]
    [​IMG]
  2. CtSebby
    CtSebby New Member
    Dec 12, 2009
    ct
  4. nhmaster
    nhmaster Master Plumber
    Jul 30, 2008
    Tech. Instructor
    S. Maine
    The circulators should have been on the feeds
    The relief valves need to be piped to within 6" of the floor
    Is that a plug in the vent opening of the back flow preventer?
    The oil line needs to be clipped up and protected
    The circulator on the indirect should not be down there on the floor.
    The wiring needs to be straightened out and attached better
    The water feed valve shoud be piped above the expansion tank.
    Where is the low water cut off?
  5. CtSebby
    CtSebby New Member
    Dec 12, 2009
    ct
    So my install says rookie all over it.
  6. Doherty Plumbing
    Doherty Plumbing Journeyman & Gas Fitter
    Jun 22, 2009
    Red Seal Journeyman Plumber & Licensed Gas Fitter
    Penticton, BC
    As long as you are pumping away from expansion tank you should be ok with the pump on the return side of the boiler. But by the looks of the system you seem to be pumping into the expansion tank.
    The boiler feed only needs to be connected below the spiro-vent to help eliminate any air the is introduced into the system a little quicker. It's just the preferred method.
    The drip in the venting could be condensing flue gases. This would not be a good thing and would most likely be caused by to low of return temps (130-140 min). Once this happens it just get worse and worse because your heat exchanger will start to get plugged up. The flue gases condense and then trap particles in the flue gases.
    Or you could have a failed rain cap on the top of the vent and you're getting rain water in the venting!
    The atmospheric port on the BFP will drip when there is a sudden change in pressures. IE if the boiler system pressure jumps quickly and the house pressure drops when someone opens a faucet. Especially where you have it piped on the supply of the boiler (hottest water temps). You're also pumping into the backflow preventer which isn't helping.
    Move the boiler feed to tie in under the expansion tank and repipe the system so that you are pumping away from the expansion tank.
  7. rmelo99
    rmelo99 Network Engineer
    Jul 7, 2006
    Network Engineer
    For your first boiler install as a Diyer I'd say its pretty good.
    Ive seen pro installs that can't even hold a flame to yours.
    These are pros here so take the critique. Not everyone does everything the same and there are somethings that eveyone should be doing the same.
    Don't be discouraged, just make some of the fixes that were mentioned to you here and you'll be closer to a Great install.
    Low Water Cutoff is code in most places...plus its cheap insurance to protect your new equipment even if its not required.
  8. frostnip
    frostnip New Member
    Jan 7, 2009
    I am no boiler expert but the one thing that I see that bugs me is the plywood where you have the electronics mounted appears to be in close proximity to the exhaust stack. I personally would ditch that and use masonry anchors.
    I'll bet you are great at sweating copper pipes now.