Natural gas valve pressure ratings and pressure testing

Discussion in 'Plumbing Forum, Professional & DIY Advice' started by pigrew, Jan 29, 2013.

  1. pigrew

    pigrew New Member

    Joined:
    Oct 25, 2011
    Location:
    West Lafayette, IN
    Hi,

    I'm planning to add an appliance to my house, and will want to do a pressure test of the newly installed gas lines. I'm getting confused about the pressure ratings of the various valves involved. My main shutoff says 175 PSI, but most of the appliance valves say either 1/2 or 5 PSI. Finally, I see a Nibco valve listed online <http://www.nibco.com/resources/ProductSubmittalDocs/GB1AGB2APV.pdf> that lists three different pressures: 1/2, 5, and 600 PSI CWP.

    For the nibco valve, does that mean that it would be able to withstand up to 600 PSI of (cold) air/gas pressure, but should only be used as a main shutoff for up to 5 PSI, and an appliance shutoff where the working pressure is less than 1/2 PSI? Should the other shutoff valves rated at 1/2 or 5 be able to withstand the 4 PSI of the pressure test?

    I plan to do the pressure test at about 4 PSI, with a gauge that reads up to 15 PSI. My biggest question is if I should cap off the lines before the shutoff valves, or close the shutoff valves and remove the caps on the traps so that excess pressure leaking through valves would be vented instead of damaging the appliance regulators.

    Thanks!
     
  2. hj

    hj Moderator & Master Plumber Staff Member

    Joined:
    Aug 31, 2004
    Occupation:
    Plumber
    Location:
    Cave Creek, Arizona
    "Excess pressure" had betten NOT "leak through the valves". If it does you have bad valves. The lines should be tested to 10 psi up to the appliance valves. Ideally, we also cap the ends of the flexible connectors and open the valves so everything is tested up to the appliance.
     
  3. Sponsor

    Sponsor Paid Advertisement

     
Similar Threads: Natural valve
Forum Title Date
Plumbing Forum, Professional & DIY Advice Natural Gas Control Valve Leak Mar 23, 2012
Plumbing Forum, Professional & DIY Advice Suggestions for converting to Natural Gas Boiler Jun 24, 2015
Plumbing Forum, Professional & DIY Advice Does a 2PSI to 0.5PSI natural gas regulator even exist? May 28, 2015
Plumbing Forum, Professional & DIY Advice Pic of natural gas line to grill / fireplace - look weird? Apr 24, 2015
Plumbing Forum, Professional & DIY Advice Tankless water heater, Electric vs natural gas Mar 31, 2015

Share This Page