May need to replace boiler – What with?

Users who are viewing this thread

Heating in Colorado

New Member
Messages
16
Reaction score
0
Points
0
Location
Colorado
I am new at this an am looking for some help and advise.

I have a Colorado 80526 2 story plus basement home which I built in 1985, all original. It is heavily insulated including triple glazing. It currently has 4 zones controlled with zone valves plus the current gas boiler does DHW. It was built to have good passive solar gain and on the current system and only uses 530 therms /year in including a gas dryer and grill. I have calculated it uses 30 therms/ mo. in summer. It requires heat only 5 month, with the maximum used in past five years 125 therms in January and averaging 74 therms per month for entire heating season. There is only my wife and I living in the house and it has 3 bedrooms with a tub and two showers. Our current gas rates are about .08 / therm plus a $10 monthly fee. We hope to be in here for many more years.

All current radiation is slant fin; I have the separate zone information. One zone is in a shop which is heated only when the area is used, which adds a sudden load of 40 degree water upon initial start up in the return. This shop has been a part of the system for only 15 years.
The system that it has been running on is a Heatmaker. This has developed a drip from the 12 gallon tank and I assume the boiler will need replaced. For the past 25+ years the basement has been kept at 72, all winter (often turned to 74 when 10 or below outside) and the 1st floor heat comes on only when the outside temperature drops enough, to come on at 70, (occasionally to 72 in evening) the 2nd floor is kept at 62 -66 and then comes on only when it is really cold, possibly below 10 and / or very windy.

I am a novice on this compared to many very experienced contractors. I am also concerned with spending a small fortune to “save energy†on a house that has cost so little for DH & DHW. I have looked around some at on demand DHW and see a lot of complaints. However, I also have been reading the forums and see many problems from a lot of Mod Coms. I am trying to be informed on what is the best way to go. Is a mod/com too expensive for the small saving I should expect? I expect I will need a side arm heater, unless there is a better idea. What about size, the Heatmaker is 120KBTU input and has always been plenty big.

My requirements seem simple, but I am looking for any input. Thank you
It must be rim joist vented. Low cost to operate. Limit up front cost, house currently only cost $160 / yr to heat & $130/ yr for DHW, $60 / yr for dryer & grill. I have more detail that can go here too.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
Every good heating system design starts with a room-by-room heat load calculation based on realistic indoor temps and the 99% outside design temp for your location. If zip 80526 Fort Collins that design temp is +1F in town, but if you live in the hills subtract 3F per 1000' above 5000'. That information will determine how much burner you actually need.

In a passive solar house it's not possible to determine the heat load based on fuel use. The information you would need for the rough cut is the "whole-wall" R-value and area of exterior wall in each room, the "whole-assembly" R-value of the roof/attic assembly (where appropriate) and the ceiling area, and the window U-factors & area. If you set up a spreadsheet with the wall/ceiling/window area & U-factor of the windows, with the wall & attic construction & R-values we can cook up reasonable whole-assembly R values to generate a U-factor for the walls & upper floor ceilngs.

The basic calculation of the heat load is:

U-factor x temperature difference x square feet= BTU per hour.

Add up the numbers for wall/window (and door)/ceiling for each room to come up with a raw heat load for the room. Add all of the room loads on each zone to come up with the zone load, and add up the zones for a whole-house load. Since the shop zone is intermittent use only, keep it separate, or only calculate it with a 45F indoor temp (or whatever temp you keep it at when not in use.)

To fine-tune it you'd have to add a fudge-factor for infiltration/ventilation rates, and subtract out interior heat sources (250BTU/hr per sleeping human, 150BTU/hr per refrigerator, etc.), but in a tight passive solar house using just the raw conducted loss numbers should be close enough.

Then you will need to measure up the linear feet of SlantFin baseboard in each zone. The ratio of heat load per foot of baseboard will determine the water temp required to deliver enough heat to cover the load.

With the heat loads and water temp requirements then (and only then) is it possible to come up with appropriate & reasonable heating equipment suggestions for meeting that load (and how to set it up.)
 

Heating in Colorado

New Member
Messages
16
Reaction score
0
Points
0
Location
Colorado
Dana,
Thank you very much for that information. I will put those numbers together.

I know the wall and upper ceiling R factor information. I am not sure on the glass, it is thermopane dubble hung windows 3" trapped air plus storm. Can I use .2 safely for the U factor of the windows? I will put that information together and come back with it. I already have the linear feet of slantFin in each room as well as in total zones on a speadsheet.

Your comment on the solar making the fuel consumption numbers ineffective, has allowed me to stop working on that chart at this time. Thanks, that makes sense.

I started this quest because the first contractor came to the house and without having any of the information you have requested here, spent 20 minutes in the house and with no consideration for anything gave me his bid for a mod con. I knew then, I needed to learn newer more current information. Thanks for giving me and I am sure other a direction to look.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
1980s vintage clear glass double panes on their own have U-factor of ~0.5-0.6. Adding a clear glass pane 3" away brings that down to U-0.35-0.4 or so. Without any low E coatings on either the double-pane or the storm window glazing, assume it's something like U-0.38.

To hit U-0.2 requires 3 panes and multiple low-E coatings, and they're pretty pricey. In a passive solar home you wouldn't normally want U-factors that low, since the low-E coatings cut severely into solar gain. At about U0.35 sealed double panes with just a single surface of low-E on one of the surfaces inside the sealed portion will usually have a fairly optimal gain/loss characteristic, gaining considerably more energy during wintertime daylight hurs than they lose overnight. Clear glass U-0.5-0.6 double panes have higher gain than a U0.35 window but they lose a lot more too.

When calculating U-factors for walls/ceilings you can't use just 1/R of the center-cavity insulation value of a studwall. The thermal bridging of the framing is significant, but the sheathing & siding adds some too. eg: A typical 2x6 16" studwall has a framing fraction of ~25% (1/4 of the area is thermally bridged by ~R6.5 studs, plates headers, etc.). With R20 cavity fill and an R1 allowance for the combined sheathing/siding/gypsum the "whole wall" R comes in between R13 & R14, with a U-factor of ~0.075 rather than (1/R20=) U0.050.

Attics and cathedral ceilings have lower framing fractions than walls, and sometimes the joists are thermally broken with insulation deeper than the joist depth.

Bottom line, to come up with realistic U-factors for walls & ceilings we'd need a description of the whole assembly, from the interior paint to the exterior paint. Passive solar homes tend to be built & insulated differently from standard code-min construction, so it takes a more careful analysis to have any accuracy at all. If stick-built, the stud/rafter/joist spacing makes a difference too.
 

Heating in Colorado

New Member
Messages
16
Reaction score
0
Points
0
Location
Colorado
Dana
Thank you on the glazing numbers and information. These are clear glass, no E coating, it sounds like I will be able to use U-0.38 for most of the windows, which are all the same construction as well as the same size. However I do have a few fixed windows which at the standard 80’s triple glazing with maybe ½” between the layers of glass. I have then added a decorative cut class in a fixed framed with 1" of air inside of that and then an additional layer of glass for protection inside of that making a total 5 layers of glass wit 2 - 1" layers of trapped air. How do I figure the U factor on that? I have two Velux skylights which show this value: U factor = .44, then there is a layer of fixed glass mounted in the opening with 6” of trapped air space. How do I figure that total U factor?

As I recall the foil backed urethane foam boar used on the entire house had printed on it that the R value was 2.38, can that be right?

Here is the exterior wall construction: Stick built 16” o.c., 2x6, 8’ ceilings. starting with interior paint/ ½” gypsum board/ 3 mill full vapor barrier/ framing w R19, non backed Owens Corning Fiberglass fill/ outside surface is covered with 1/2” urethane foil double faced board. US Steel siding with no additional backer insulation. All seams of foil board are sealed, all windows, doors electrical boxes and plates had urethane foam seal added to slow infiltration.I am not sure how to figure this total wall when the urethane covers the outside of the studs.

Here is the 2nd floor ceiling construction: No cathedral ceilings in the house area. Trusses made of 2x4 constructions, 24” o.c., starting with interior paint/ ½” gypsum board Blown in Owens Corning small all fiberglass cubes to R 40 when new. Added on top across the direction of the trusses with additional filling at truss bracing was R19 Owens Corning with no backing. The area has adequate ventilation with a power vent for summer use.

There is a 4’ wide front & back roof on the 1st floor that makes up unheated area above. Here is the construction: Sick built 2x6 constructions, 24” o.c., starting with interior paint/ ½” gypsum board bats fill the area as much as possible to allow ventilation above. That makes it first R19 covering the entire area, then the upper half another layer of R19. So half is R19 and half of the area is R38. This total length is 38’ which will need to be included in the 1st floor planning. I think I can figure this okay.

The finished basement walls are ; paint ½” gypsum board, 1-1/2’ urethane with 2x2 16”o.c. striping then 8” poured concrete, on the exterior all basement walls, they are covered with 2” of urethane. The rim joist is R19 Owens Corning bats.

The unfinished basement walls ; do not have the interior insulation, 2x2 nor drywall, so that will be easy to figure, but mostly subsurface with I suppose a constant of about 55 degrees below 2 feet.

It has been a while since I have figured any of this stuff! Thanks for your help.
 

Heating in Colorado

New Member
Messages
16
Reaction score
0
Points
0
Location
Colorado
I have calculated the total wall R values for all of the combinations in the house. I used the charts from www Colorado energy.org which was much easier to use from this site: http://www.allwallsystem.com/design/RValueTable.html

I assumed that since near 10% of the wall is stud in a 16” o.c. application the built R value of the wall was 90% of the Total Wall R value and that 10% of the wall was the R values where the studs are in the wall. I came up with the average. Now I will calculate the ceilings the same way, unless someone gives me a reason to believe that that this is not correct. This gave the worst U value in the house as .042845 in this solar assisted home. No considerations are made for solar gain.

I now need a program that allows me to insert all of the information for the walls, windows etc to arrive at the totals of each room and then the house. Any recommendations?
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
I have calculated the total wall R values for all of the combinations in the house. I used the charts from www Colorado energy.org which was much easier to use from this site: http://www.allwallsystem.com/design/RValueTable.html

I assumed that since near 10% of the wall is stud in a 16” o.c. application the built R value of the wall was 90% of the Total Wall R value and that 10% of the wall was the R values where the studs are in the wall. I came up with the average. Now I will calculate the ceilings the same way, unless someone gives me a reason to believe that that this is not correct. This gave the worst U value in the house as .042845 in this solar assisted home. No considerations are made for solar gain.

I now need a program that allows me to insert all of the information for the walls, windows etc to arrive at the totals of each room and then the house. Any recommendations?

Were you walls just infinitely long studs, with no jack studs, king studs, bottom plates,doubled-up top plates, window & door headers & framing etc, yes, you'd be at about a 10% framing fraction. In the real world walls have finite height, and they have windows & doors & wall lengths that don't align perfectly with top & bottom plates. This has been surveyed to death by building designers for decades- typical framing fractions for 16" o.c. spacing average around 25%. They can hit 30% or higher where mid-wall fire-blocking or seismic reinforcement is required, maybe as low as 20% for balloon framing with the window & door size & placement are carefully selected to align with the standard stud spacing, and only single thickness plates & headers used. Using a 10% framing fraction your heat loss number will be wildly optimistic. Unless you've added it all up from the original blue prints, assume 25%- it'll be close enough.

If you use an Excel or Open Software Foundation spreadsheet tool, set up a room by room blocks of cells to do the numbers something like:

Kitchen

__________ U-factor _x_ area__x__design delta-T_=_heat loss

Windows: ____0.38_____10.5'_______68F_________271 BTU/hr

Doors:_______0.50_____22'_________68F_________748 BTU/hr

Wall: ______0.057_____127'_________68F________492 BTU/hr

Ceiling:__ __0.023_____154'_________68F________241 BTU/hr

Room total:_________________________________1752 BTU/hr

Dining room (etc.)

Then add up the subtotals of for all the rooms in each zone, and the ratio of BTU/foot of baseboard for the zone. Add up the heat loads of all the zones to come up with the whole-house total heat load. (Assume the shop zone to have a 45F interior temp to account for the intermittent use aspect.)

Calculate the "whole-wall" R values carefully (or give me your stackup and I'll hand off something close enough), and use 1/R for the U-factor. Do a similar calc for the attic/ceiling to come up with a U-factor for the upper floor ceilings.

When you have the whole house load and the ratio of BTU/foot-hour for the baseboard, the range of solutions can be weighed.
 

Heating in Colorado

New Member
Messages
16
Reaction score
0
Points
0
Location
Colorado
Dana
I understand the fact that the wall is not really 10% stud when just simply plates, headers, jack studs, and electrical boxes are added into the wall. Something that may make these walls a little different than normal is the fact that everything is covered on the outside with Foil-faced Polyisocyanurate 1/2" which has an R value of 3.6. Also there are not a large number of windows, but rather larger windows. There is no fire-blocking or seismic reinforcement, plywood corner bracing is done with metal T reinforcement. Maybe using 25% will be good enough. that is what i willl use unless you suggest otherwise.

Some other things that will be different than normal… 1.) There is a south facing 36’ long wall that has a 4’ x9’ of trapped air with another wall enclosing that area which is casement triple glazing starting 36’ from the floor up to the header, there are 5 posts framed between the windows. There is a brick wall for mass on the house side of that room, as well as a cement floor. This area is not heated except by the sun. The purpose of this room is only to provide solar gain heat. (More importantly a toy room for grandchildren they say!) My guess was to treat the interior wall of that room as though it has over 12” of trapped air then what ever the R factor would be for that mostly glass wall, but that does not account for the ceiling heat loss. I will leave that up to you to decide.

2.) There is a glass enclosed porch on the east side of the house with a 22’ long wall that is much the same thing as the solar room but without the cement floor and brick mass wall. This area does have a vaulted ceiling

I will begin to put these numbers together on the spreadsheet. I will come back to you when I have one area together to see if you agree with my information.
Thanks for all of your help.
 

Heating in Colorado

New Member
Messages
16
Reaction score
0
Points
0
Location
Colorado
Here are my calculations for the second floor bedroom/ bathroom areas. I have included the closets and bath in each area, as well as the 10' hall. The 2nd area is two adjacent bedrooms and bath. This area is seldom heated with the baseboard except when below 10 outside, and that means zone below is running too. The heat loss from below provides most heat. There is nothing in this calculation for the stair that comes from below, but the stairs area is included in the square feet of this floor. I hope this table comes through in a legible format.

MBR w bath & closet
__________ U-factor _x_ area__x__design delta-T_=_heat loss
U factor area delta T BTU/ HR
Windows 0.38 49.5 71 1335.51 BTU/HR
Doors 0 0
Walls 0.0464738 397 71 1309.957012 BTU/HR
Ceiling 0.016764459 379 71 451.1148365 BTU/HR
skylight 0.38 4 71 107.92 BTU/HR
ceiling fan 0.540540541 4 71 153.5135135 BTU/HR
Room total: 3358.015362 BTU/HR[/B
]Total Slant Fin= 12'


Br 2 & 3 w bath & closets
__________ U-factor _x_ area__x__design delta-T_=_heat loss
U factor area delta T BTU/ HR
Windows 0.38 27.8 71 750.044 BTU/HR
Doors 0 0
Walls 0.0464738 397 71 1309.957012 BTU/HR
Ceiling 0.016764459 379 71 451.1148365 BTU/HR
skylight 0.2331 4 71 66.2004 BTU/HR
Room total: 2577.316248 BTU/HR
Total Slant Fin= 10'


BTU Loss for total upstairs: 5935.33161
This area is one heat zone

I have figured how to calculate the heat loss to the sun room and porch area. I know the minimum temperature in these rooms, just like the shop. So the Delta T in the shop is 25, the delta T to the sunroom is 35, and the delta T to the porch is 45. So I just use the regular wall construction U factor and us the different Delta T for these areas. Dah!
 
Last edited:

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
Foil faced iso on the exterior is a standard construction these days- even enshrined in building codes. (In places where R20 is required for 2x construction R13 2x4 + R5 exterior foam is a code-accepted alternate.)

When calculating the whole-wall R it's safe to calculate the assembly without the foam layer, then add it's R value at the end. But don't assume R3.6 is the right number to add: Polyiso drops with R value with falling temperature. Half-inch iso on the exterior will be no better than ~R3 at 0F for purposes of heat load analysis.

With a 12" air gap between the glass and the brick wall, you can't count the air films in that trapped space, since it will have strong convection turbulence breaking them up. You can still count the air film on the conditioned space side, but not the exterior (it doesn't take much of a breeze to break it up on a residential sized wall assembly.)
 

Heating in Colorado

New Member
Messages
16
Reaction score
0
Points
0
Location
Colorado
When I built my first house in 1971, in 44720 Ohio, my mentor told me I was stuffing money down a rat hole by making the ceiling R19 instead of R13. He told me I would never recover the cost in the sale. He only built custom homes. We built side by side equal houses and he told me I would not recover one cent more if I did that. I also added additional outlets. He was right! He built and sold two and I had not sold my first one yet! Boy have things changed!
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
DYA think? <LOL>

Gas isn't 15 cents/therm any more and heating oil is WAY over 25 cents/gallon!

Code min in MA right now is R38 attic, R13+5 (or R20) walls, R10-foam ( or R13 batt) on the foundation walls, and R10 foam sub-slab.

When MA finally goes to IRC 2012 the attic-R min bumps up to R49, the walls stay the same as does the sub-slab R, but the foundation goes to R15 foam/R19 batt.
 

Heating in Colorado

New Member
Messages
16
Reaction score
0
Points
0
Location
Colorado
Dana

Well, I am certainly glad to see that someone has figured that out since I began building.
I have a couple questions on my heat loss calculations. In the basement area, I have not added in any loss to the floor above at this point. I understand that that does affect the heat loss for the room, but for the house. I have also done the same for the 1st floor loss to the second floor. There is nothing in the calculations for the stairs between the basement, 1st & 2nd floor. Is it okay to leave it that way? I understand that the total heat loss for each area below will be greater.

In the basement only part of it is heated, the other part has the Heatmaker and that puts off enough heat to not see a great difference. Possibly a lower BTU more efficient furnace will require some added radiation area. So the loss between these areas is not considered.
Some creature comfort comments: Remember that in the past 25 plus years, the basement has been kept warmer, than the 1st floor and the 2nd floor cooler yet. This allows the Zone 3 on the 2nd floor to only come on when it is pretty cold and other zones are normally running too. Just some thoughts as to hoe I have lived with the system. It is a tight house and I tend to be a very warm person, thi=us I prefer to sllep in the cooler 2nd floor area.

In the shop area which is only heated on occasion for the common wall with the house, I will have a heat gain from the house, how is that figured? Do I take the loss from that wall and add it as a gain for the shop?

I have not calculated the shop numbers yet.

There is a stairs going from the basement to the shop in the shop area. The shop is far undersized in radiation, so that 4’ door from basement is opened to raise shop temperature faster when heat is needed, since the radiation in basement is so over sized.

I currently have the following numbers in total for the area by each zone. All Slant Fin is ¾” except in basement area where it is ½”. I can give you greater breakdown if you believe there is a problem.

Basement finished area
BTU Loss/ Hr = 422
Slant fin = 14’

Basement unfinished area
BTU Loss/ Hr = 674
Slant fin = 0’


The above is Zone 1 Basement
BTU Loss/ Hr = 1096
Total Slant fin = 22’ (1/2”)


Next Zone:

Living Room & Entry
BTU Loss/ Hr = 2484
Slant fin = 13’

DR & Kit
BTU Loss/ Hr = 2601
Slant fin = 19’

Office
BTU Loss/ Hr = 843
Slant fin = 9’

Entry & ½ ba
BTU Loss/ Hr = 1570
Slant fin = 5

The above is Zone 2 1srtFloor
BTU Loss/ Hr = 7497
Total Slant fin = 46’


Next Zone:

MBR & bath
BTU Loss/ Hr = 3314
Slant fin = 12’


BR2, BR3 & bath
BTU Loss/ Hr = 2560
Slant fin = 10’

The above is Zone 3 2nd floor
BTU Loss/ Hr = 5874
Total Slant fin = 22

Next Zone:

Shop Zone #4 will go here when completed
 

Heating in Colorado

New Member
Messages
16
Reaction score
0
Points
0
Location
Colorado
Dana
I have calculated the shop heat loss using this method. I used the common wall with the house as a heat gain the same as the loss from the house. I did not calculate any loss for the concrete floor which is on grade. Should that be added in as R of concrete with the delta to the earth?

I used delta 41 since the heat is kept at 40 when not used. When the area is heated I do not use it if the outside temperature is below 20 and then only heat it to 60 thus making the delta T still 41. So as I see it, the Delta T is always 41 for design. Do you agree with this?


The Slant fin in the shop is only 20', which is low when trying to raise the temperature 20 degrees for use.

So if all of this is correct, that shows the total loss for the everything at design temperature of -1 as follows:

House BTU loss
Basement 1096
1st Floor 7497
2nd floor 5874
Shop 2900
TOTAL 17367


Your thoughts? I can give you how anything is calculated as a cross check, os specifics of the construction.
M
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
For our first-cut purposed the loss through the slab to the ground is pretty negligible- within the margin of error.

So your zone totals are"

Zone 1: 1096 BTU/hr, 14' of baseboard, or 78 BTU/ft-hr

Zone 2: 7046 BTU/hr, 46' of baseboard, or 153 BTU/ft-hr

Zone 3: 5874 BTU/hr, 22' of baseboard, or 267 BTU/ft-hr

Total heat load (except shop): 14,016 BTU/hr <<-seems on the low side for a house with a lot of glass, but not super-low, given the 530 therms/year number.

Adding a 25% fudge-factor for below-grade losses, ventilation & infiltration air etc and the whole house load is still looking like ~17,500 BTU/hr, which is a tiny load- a modulating condensing boiler would be a waste here: The whole house load is barely above the minimum-fire output of most mod-cons, and the load of even the highest loss zone (zone 2) is about half the output of the smallest in the line of most mod-cons. Worse yet, only Zone 2 has enough radiation to keep a mod-con boiler from short-cycling with 120F output temps (where it needs to be to break into the mid-90s for efficiency.)

Adding in the 2900 BTU/hr (145 BTU/ft-hr on the fin-tube) of the shop you're still at only ~20 KBTU/hr. (And yes,the 41F as-used delta-T is the right way to run that calc.)

Taking your worst-case load/ baseboard number (zone 3) and applying the same 25% "all of the rest" factor it's looking like (1.25 x 267=) 334BTU/foot of baseboard. Consulting a SlantFin output spec, that zone will need an average water temp (AWT) of about 140F on design day, the others could get by with 120F. Assuming a 20F delta-T on the zone-3 baseboard you would need 150F water.

Even the whole-house load is too small to keep from short-cycling a 3-plate forced-draft mid-efficiency cast iron boiler.

The fossil-burner approach to this that works would be a power drafted combi-hot water heater internal heat exchanger, but you'd be advised to add more radiation to Zone 3 to get it's load/length ratio more in line with zone 2, getting the max water temp down to the domestic hot water temperature range. The thermal mass of the water in the tank keeps the burner from short-cycling, and if you add enough radiation to Zone 3 to where it can heat the zone at 120F AWT you can just set the tank to 130F-140F and forget about it.

For more money you could get condensing efficiency by going with a Vertex or Polaris hot water heater, but that would require a bit more system design work and the added expense of a bronze-impeller pump & heat exchanger.

If there isn't sufficient free wall for baseboard on the Zone 3 to just add more baseboard (proportionally, about 1.6-1.7x what's currently there) to get the total length up to something like 35-40', you can still get there with small panel radiators, which have a greater comfort factor than fin tube, but are considerably pricier.

It may not work out as well depending on the floor plan layout, but your heat load is within the 0F output of a 1.5 ton ductless mini-split/multi-split. A good 1.5 ton mini-split will have an operating cost comparable to heating with a power vented Combi-2 hot water heater, and would have the additional benefit of high-efficiency air conditioning. But since it's a point source (or multi-point source) heating system, the individual heat loads of doored-off bedrooms might need supplemental heat to keep the comfortable at 0F with the doors closed. In my neighborhood a good 1.5 ton single head unit runs ~$4-4.5K installed, but with a mostly DIY approach it's about half that. A 2- head 1.5-2 ton comes in around $5-5.5K. As currently zoned #2 and #3 have sufficient load to warrant an individual head, but if you leave all the doors open you'd be able to heat them with a single head, if the convective paths are reasonable. (You'd still have to figure out what to do for hot water too.)

If it were my place I'd be inclined toward a Vertex or Polaris condensing hot water using the Taco X-Pump Block pre-engineered potable/heating isolation, and adding panel radiators to the bedroom zones, but that's a significant cost up-tick from a Combi-2 plus additional baseboard. The LAST thing you'd want do to is install an expensive mod-con boiler or low-mass combi heater and short-cycle it into an early grave. A tiny cast-iron Burnham ESC-3 power vented boiler and a bargain-basement electric hot water heater (not wired up) impressed into service as a buffer tank could work, but it takes a bit of design & tweaking to get right, and in the end would only be marginally more efficient than a Bradford White Combi-2.
 

Heating in Colorado

New Member
Messages
16
Reaction score
0
Points
0
Location
Colorado
Dana,
Some initial thoughts on your comments;
I believe that the low heat loss is due to the fact that it is partially an envelope with a second wall on the south side. The entire outer wall is glass 5 ft in height the length of the wall, or about 150 sq ft of glass. That room often exceeds 96 F on a extreme sun mid winter day. It is currently over 90 in October and I am venting to the outside. As the sun angle gets better it will take in a lot more BTUs too. The next wall which is 4’ north is a heat sink and a couple windows to the living area plus an 8’ slider. The house has only 9 windows which are only 16.5 sq ft each, 4 facing east and 5 facing west. There are also three small windows with 5 layers of glazing. The ceiling has a ridicules amount of insulation partly because a friend in the business one day came by and gave me an additional layer of R 19 added to the already well insulated ceilings in return for a favor. I suppose that explains the low BTU loss even without low E glass.
I figure the 4th zone must also always be added into the total load due to the fact that it is heating when the temperature drops.

As for changing the radiation of zone 3, your are suggesting adding 13 to 15’ additional radiation making the total 35 to 37’ to the load? Somewhere in this brain, I seem to have forgotten some of these calculations. Isn’t the BTU/ft-hr you have calculated the BTU loss for the zone per ft of radiation? Or are you using the slant fin numbers for the different temperature?
Remember Zone 1 is only ½” pipe.
Just to throw a curve here, in that zone 3 area, there could be some radiant heat added beneath the bathroom stone floors, it could be a pain because the joists run the wrong direction. There is piece of drywall there that may need replaced anyway. Just a thought here, I have never worked with that. I am too old, or it is too young!
So far, there are several possibilities you have mentioned. The Bradford White 72 Gal - 76K BTU, Polaris hot water heater, Vertex, and you even mentioned the Burnham ESC3 with a hot water tank plumbed into the system. So my question at this point is why do you prefer “If it were my place I'd be inclined toward a Vertex or Polaris condensing hot water using the Taco X-Pump Block pre-engineered potable/heating isolation” Should these system be more efficient? How about trouble free life span expectations. I need to study these systems farther and will be back to you soon, probably with more questions.
This house had AC installed a few years ago. It is a fan unit in the attic with the compressor on the roof, 10 ft away. Duct was run to the upstairs bedrooms from above and one duct through a closet straight below to feed the first floor, as well as a return on 1st floor. The 2nd floor return is on the ceiling in the center of the 2nd floor. As long as all upstairs doors are open and one office door on the first floor is closed, the temperature is balanced to within about 1 degree, bedrooms being coolest.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
I calculated the ratio of the heat loss of the zones to the length of fin tube in each zone. Zone 2 as-is would be able to meet the load at the 99% outside design temp with 140F (or cooler) water according to SlantFin's charts. but zone 3 was still needed more to come into line. If the peak water temp requirement is 140F it means you can run it off a hot-water heater at a standard storage temp.

The Vertex/Polaris would use about 12-15% less fuel than the Combi-2, the smallest forced-draft Burnham cast-iron (ESC3) would use about 8-10% less fuel than the Combi-2.

The size of the pipe makes little difference whether 3/4" or 1/2"- you aren't bumping into any design limits. Adding 15' to zone 5 has negligible impact on the pumping head/flow rates.
 

Heating in Colorado

New Member
Messages
16
Reaction score
0
Points
0
Location
Colorado
Dana,
In understanding how the house currently heats, I know that the Zone 3 (2nd floor) is seldom on, but we are coming up with a need for additional radiation in that area I have gone back to look at my heat loss numbers for each area. I have seen that I did not add in heat loss / gain from the ceilings between floors. The only ceiling heat loss consideration is for the loss through the ceiling when it goes to the outside.

I looked at these numbers again. I know there should there be heat loss from the basement through the ceiling to the first floor. But I also know that there is only a slight temperature difference. So I went ahead and added in those ceiling loses to each area, knowing it would not be a large number. Understandably, it lowered the heat loss of the zone 3, 2nd floor as well as the raised the loss of Zone 1 and 2 slightly.

Here are the slightly corrected loses:
House BTU loss
Basement 1477 w 16’ of slant fin
1st Floor 7844 w 46’ of slant fin
2nd floor 5146 w 22’ of slant fin
Shop 2900 w 20’ of slant fin
TOTAL 17367 BTU loss/ hr


Now, let’s see if I have this right…I have added 25% BTU loss for slab, infiltration etc. which was not in the BTU loss numbers. I then calculated the ratio of the loss to the feet of baseboard by dividing the BTU loss by the number of feet in each zone.

Z1 = 1846 BTU loss per hr /16 ft slant fin = 115 BTU/ft - hr
Z2 = 9805 /46’ = 213 BTY/ft - hr
Z3 = 6432 /22’ = 292 BTU/ ft-hr
Z4 = 3625 /20’ = 181 BTU/ft\hr
Adding 12’ to Z3 will makes it
Z3 = 6432 /32’ = 201 BTU/ ft-hr


130F water in slant fin is 260, 140 F is 320
As I see it, operating this at 130 is too cool at 99% outside design temperature, but is fine at 140 on all zones, with Zone 2 being the most demanding. Is that how you see it too? Operating at 130 will work when the outside temperature is warmer. I understand this system has no remote sensor for auto set back.

I have done some looking at the Polaris and so far, it looks like they type of system I need. So the question at this point is how I determine the size of this hot water heater now that we know the space heating needs. I know on normal hot water heaters the sizes used for a 3 bedroom, 3 bath, home would possibly be 60 gallon and the BTU output will determine the recovery rate. But I am not so sure of either the tank size needed nor the BTU rating needed.
I found this on line link which looks like a simple install example: http://solarhomestead.com/best-off-grid-heating-system/

I will look at this and other systems we have discussed in more detail too, but I am sure liking what I see in the Polaris so far.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
You're on the right track. Bear in mind that the SlantFin output is average water temp, not entering water temp. To hit 130F AWT you'd be looking at boiler/heater output of ~140F.

The Polaris based system in your link uses potable water in the heating system which isn't advisable (or even legal, in many locations) for health reasons. (Water stagnating in the heating system tubing between 80-110 can grow legionella and other fun stuff.) To use a Polaris or Vertex requires an external heat exchanger and a potable-tolerant pump for isolating the potable from the heating system water.

best.jpg


^^^ not this^^^

This:

image016.png



If going with Polaris you can the tank to the largest tub you need to fill. The burner on even the smallest Polaris is enough to heat your house and take a never-ending shower.
 

Heating in Colorado

New Member
Messages
16
Reaction score
0
Points
0
Location
Colorado
Dana
I here you on the Legionnaires stuff! I believed that this pictured system was not considering that, and the main reason I sent it to you. Although, they are circulationg all DHW through the heat zone, it would not work with zone valves.

So my next question is about heat exchangers. How efficient? Size for the heating needs of the house? Quality? Brands that are better? Whatever else, that I do not yet know and need to!

Back to the slant fin. I may need to add additional feet to the Z2 area too, since at 120 it is 210 BTU/ft-hr. There is still additional loss from this are with an open stairs to above. But that can be determined later too, since the numbers are still okay.

System from you as shown. It looks as if this will need a circulator with shutoffs, a one way valve, and temperature sensors. I may be able to connect into my current stem without major work. It is just a secondary zone add here that is currently a part of the heatmaker boiler.

System size seems to be the smallest Polaris 34 – 100. That is their smallest unit. There is only one bath tub in the house, a standard Kohler cast iron, currently only used by grandchildren occasionally. All three bathrooms have showers.

So far, to me, this seems like the best possibility by far. How many problems are people having? I see that igniters are a problem. I had that problem in conventional forced air systems I had maintained. The best solution is to always have one or two on hand. I am more concerned about circuit board system failures. I know enough about them to understand what is causing most failures since my wife was in the circuit board manufacturing business a couple decades with a very large company. Gas valves are gas valves, and should not fail easily. Sensors should be easily diagnosed and replaced.

On the Heatmaker the number one failure was the on board Grundfos circulation pump, about 10 in 28 years. The igniter failed about 6 times. The temperature sensors failed occasionally. Considering how complex the system was, I believe that it did quite well. The whole house Taco circulator pump failed once, just a few years ago, All of the original Honeywell zone valves are still in place. Everything is isolated with valves. It seems that I can pretty much hook into the current system. I may replace all of the valves with ball valves. So the system must be pretty much torn apart in order to do that. Maybe I should consider replacing zone valves and other things too. What are your thought on that?
 