    I just purchased a new house with a Hunter Pro-C system. I had included a request that the unit was winterized in the purchase of the house.

    I am trying to set things up and when I turn the water valve on, there is water shooting out of the top of the main water valve (there is a black plastic ring on the top). This happens if the Hunter system is on or off. So - I have the main to that pipe permanently off and can't use the system until I resolve this (and the local landscaping guys don't seem to return calls...)

    Any advice would be MUCH appreciated!
  2. Verdeboy

    Verdeboy In the Trades

    Messages:
    2,051
    What do you mean by "main water valve"? Is water coming out of your vacuum breaker? (See attached sketch).

    Maybe the pressure vacuum breaker was partially disassembled during winterizing and you need to put it back together. Just a guess.

    Attached Files:

  3. Nate12

    Nate12 New Member

    Messages:
    3
    Yes - it is coming out of the top of the plastic piece in that vacuum assembly. Thanks for the help.
  4. Wet_Boots

    Wet_Boots Sprinkler Guy

    Messages:
    798
    Location:
    Metro NYC
    Winterizing may not have been performed, or maybe a shut-off valve was leaking. Continuous water from the top of the Pressure Vacuum Breaker may indicate broken plastic parts.
  5. hj

    hj Moderator & Master Plumber Staff Member

    Messages:
    26,631
    Location:
    Cave Creek, Arizona
    leak

    It froze and broke the inside piece. Usually you can repair it with a new cap and float, but if the body was distorted you need a new valve.
  6. Nate12

    Nate12 New Member

    Messages:
    3
    Thanks everyone. I will check it out. Appreciate it.
  7. Mr_Pike

    Mr_Pike New Member

    Messages:
    136
    Location:
    Nebraska
    Like to see some follow up here, as I suspect that freeze damage is not the case. I get these calls every spring from new homeowners.

    Close all the valves on the PVB before opening the main supply valve.

    Open the upstream valve (closest to supply valve) first. Quickly. You should hear a slight pop. This is setting the spring and rubber seat. If the second and downstream valve is open, it is not providing enough back pressure to seat the ring, and water just dumps out of the PVB.

    Open the down stream valve slowly, as not to cause a low pressure state and reopen the dump valve. By the way, you should have one of the lateral valves open to allow the compressed air to escape the system.

    When the pressure equalizes against the heads, open the valve all the way.

    You should be set til fall. If you are using the valves on the PVB to shut off the system, use the down stream valve. Or you could have the low pressure - filling the lines - dump valve opening problem again.
  8. hallnjcpa

    hallnjcpa New Member

    Same problem here

    I have a Hunter Vacuum Breaker as you show in the diagram. I have replaced that guts and tried opening the valves in the sequence you indicated. Still have water coming out the top. Any suggestions, at $100+, I hate to have to replace it.

    Thanx
Similar Threads: Main Water
Forum Title Date
Irrigation / Sprinkler Forum Connecting irrigation to water main with pex homerun system Apr 11, 2012
Irrigation / Sprinkler Forum Shuttering sound at water main? May 20, 2008
Irrigation / Sprinkler Forum Watermain Size Apr 14, 2007
Irrigation / Sprinkler Forum Connect to main Dec 13, 2012
Irrigation / Sprinkler Forum Repipe the main line? Apr 10, 2012

Share This Page