    When you have an outdoor main disconnect; and the main panel is separate from that (indoors), is the main panel treated as a subpanel as far as neutral/ground bonding?

    Where in the NEC do I find this?

    Just looking for a quick answer. I was asked this, and I don't know the answer.
  2. Speedy Petey

    Speedy Petey Licensed Electrical Contractor

    Messages:
    996
    Location:
    NY State, USA
    Yes, the panel would be treated as a "sub-panel" with the neutral not bonded.

    Here is the NEC section:

    250.24(A)(5)Load-Side Grounding Connections. A grounded conductor shall not be connected to normally non–current-carrying metal parts of equipment, to equipment grounding conductor(s), or be reconnected to ground on the load side of the service disconnecting means except as otherwise permitted in this article.
  3. Nate R

    Nate R New Member

    Messages:
    472
    Location:
    Milwaukee, WI
    Thanks! My brother is a home inspector. He's doing a pre-sale inspection for the seller to be able to show buyers, and to tell the sellers what may come up and be an issue, etc. He asked me about this, but I wasn't sure.

    And thanks for the code section for the quote! :D
  4. VinceS

    VinceS New Member

    Messages:
    1
    That's the problem with home inspectors!

    "Thanks! My brother is a home inspector. He's doing a pre-sale inspection for the seller to be able to show buyers, and to tell the sellers what may come up and be an issue, etc. He asked me about this, but I wasn't sure."

    Nate R, I realize it was your brother who asked the question, but doesn't that strike you as being a major problem? Your brother is a home inspector and he doesn't know the answer to that question? Unfortunately I've used home inspectors on at least two home purchases, and although they had slick marketing and reports they simply did not know what they were talking about. Unfortunately your brother seems to be in the wrong line of work...that is if he cares about providing a valuable service to his customers.
  5. hj

    hj Moderator & Master Plumber Staff Member

    Messages:
    26,843
    Location:
    Cave Creek, Arizona
    inspector

    At least he knew enough to ask the question. Most would not bother with it unless it was something that hit them between the eyes with a 2x4.
  6. drick

    drick In the Trades

    Messages:
    392
    Ain't that the truth!
Similar Threads: Main Disconnect
Forum Title Date
Electrical Forum discussion & Blog Main Disconnect Question Jan 19, 2009
Electrical Forum discussion & Blog 50 amp main breaker panel? No such animal Mar 26, 2014
Electrical Forum discussion & Blog What make/model box is this? Is it even a main or is it a sub panel? Jan 19, 2014
Electrical Forum discussion & Blog Wires from Main panael to Subpanel in two separate raceways? Aug 15, 2013
Electrical Forum discussion & Blog Grounding Rod for Main Panel Apr 26, 2012

Share This Page