leaking temp/relief valve
Discussion in 'Water Heater Forum, Tanks' started by trw888, Mar 22, 2011.
  1. trw888
    trw888 Member
    Sep 23, 2009
    Tucson
    Hi,
    I did a search for the problem I'm having and I'm pretty sure I've found the problem. But I just want to confirm that I'm correct.
    I've got a Bradford While 40 gallon gas water heater. It was installed in May 2010 by a pro. Today, I opened up the water heater closet door to find the floor was quite wet and water dripping every few seconds from the copper pipe that extends down the side of the tank. Am I right that it's the temperature pressure relief valve that the pipe is connected to and that this valve has gone bad?
    Seems hard to believe it would go bad on such a new tank...
    Thanks, Tim
  2. trw888
    trw888 Member
    Sep 23, 2009
    Tucson
    I forgot to add -- in case these things matter -- that the water coming out of the pipe is cold. There's no difference in water pressure nor lack of hot water inside the house. And we have a Watts recirculating pump on the heater
  4. LLigetfa
    Feb 6, 2011
    Information Technology
    NW Ontario, Canada
    If you have a checkvalve in your system and no expansion tank, it could well be the TPR valve is doing exactly what it's supposed to. Open a tap just enough to sustain a drip and see if the TPR valve stops relieving.
  5. jadnashua
    A T&P valve will open for three reasons: the water temperature exceeds it's safety limit (not your problem, if your water isn't excessively hot), the pressure excees it's safety limits (possible), or, it is worn out or defective. Sometimes, mineral deposits can prevent the valve from closing if it was opened in the past for a valid reason.
    So, the recirculation system won't raise the pressure enough (if at all) to open the valve. BUt, it could cause the WH to run more often, and if you do have a closed system (like mentioned), then if you don't have a working expansion tank, the pressure is too high. Water doesn't compress, and when heated, expands. If there's no place for it to go, the pressure rises dramatically, until something gives. This is often the T&P valve. Sometimes, it's a toilet fill valve, or maybe the washing machine hoses, or faucet hoses, or maybe hammer arresters, but that now 'bigger' water needs somewhere to go. The solution is an expansion tank, normally, unless the valve is bad.
    If it's only a few drops, over the length of the pipe, it could cool off, unless the flow was fairly high.
  6. trw888
    trw888 Member
    Sep 23, 2009
    Tucson
    Thanks for the replies. I tried the drip test. Maybe I didn't let it drip long enough, but it didn't appear to make any difference. I should note as well that a roughly 2' X 5' area of the floor in the water heater closet is quite saturated. I know for sure the dripping started no more than a week ago so it's dripped a fair amount of water. It sounds like an expansion tank is in order. Any thoughts on why this would happen all of a sudden? We've never had a problem like this before.
    Thanks again.
  7. LLigetfa
    Feb 6, 2011
    NW Ontario, Canada
    How much the expansion will spike the pressure will depend on several factors. The more hot water you use at once, the more there is to heat and expand. Any water use over the course of time can bleed off some of the expansion. That was what I was attempting by leaving a faucet dripping. The water use can be an automatic humidifier on a furnace, an ice maker, etc. If the humidistat has not called for the furnace humidifier, and/or ice making or other uses are sporadic, there is opportunity for the pressure to spike.
    Then again, it could be as Jim said, namely that there was a valid reason at one time for the TPR valve to relieve and it has not reseated. It is also possible that it has had a very tiny leak all along and built up with corrosion and mineral that has since pushed it further open.
    I am on a well system with an expansion tank so my old tank had no valid reason to ever pressure relieve but when we were pulling the tank, I tried to trip the TPR valve to let air in so it would drain faster, only to be surprised that it was frozen shut from corrosion and mineral buildup.
  8. Gary Swart
    Gary Swart In the Trades
    Sep 1, 2004
    Yakima WA
    The check valve mentioned can be in two places. A pressure regulator valve or a check valve in the water meter. Some cities are installed meters with check valves to prevent back flow of water into their mains. These are relatively new, so unless the city has changed you meter quite recently, that is not likely the problem. The most common place for the check is in the PRV although there are some newer models that allow bypass. While it is always possible that the T/P is defective, but you had a new on installed with the new water heater, so it is highly unlikely for that to be the problem. If you have a closed system (PRV or check valve) you must install a thermal expansion tank. I learned this lesson several years ago when I installed a PRV. After changing T/P valves 3 times, I learned about expansion tanks.
  9. trw888
    trw888 Member
    Sep 23, 2009
    Tucson
    Thanks everyone for the great insights. It sounds like I need an expansion tank, and it doesn't sound like it's a huge deal. I've the plumbing company that installed the tank coming out tomorrow.
  10. trw888
    trw888 Member
    Sep 23, 2009
    Tucson
    Just to follow up with the outcome...It turned out to be the t/p valve after all. It was covered under the manufacturer's 6-year warranty on parts and the labor was covered under plumbing company's 1-year warranty so it didn't cost me a thing.
    Thanks again.
  11. ballvalve
    Dec 28, 2009
    northfork, california
    The guys here should have told you that you had a leaking T&P, not a over pressure issue when you opened other taps and it continued to leak.
    He didnt have a leak previously, and no one changed his plumbing, and a PRO installed the heater WITHOUT a ex. tank, so Sherlock would go direct to the valve seat.
    Hopefully you didnt waste your money on a expansion tank.
    And I'll bet if he opened and closed the 'defective' T&P several times, it would have seated and stopped leaking anyway.
  12. jadnashua
    I listed a defective valve as one of the three ways the T&P leaks...
    If the utiity did any work at the street, they may have installed a check valve that the user had no knowledge of, so it doesn't have to be all internal to the home.
  13. Terry
    Aug 17, 2004
    An expansion tank will improve the performance of the water system in the home. Less drop in pressure when a faucet is used.
    I look at the expansion tanks as an upgrade. I love em!
    I also change the oil in my car every so often too. So if the tank needs replacing at some point, I don't worry about it like Ball Valve. It's a part, and parts get used up, and then you replace them when needed. There is no such thing as a home that never needs maintenance. Even if you get your water from a creek with a bucket, you need to maintain the path.
  14. Furd
    Furd Engineer
    Jul 3, 2007
    Retired energy systems engineer
    Wet side of Washington State
    Great response, Terry!
    I want to add that the handle on the T&P valve is there for a reason and that reason is not to open the valve to break the vacuum while draining the tank. T&P valves should be tested (by pulling the handle) every six months or so. Pull the handle and hold it for several seconds to flush out the valve and passages and then let it "snap" shut. Don't just "tease" it open a little bit and then slowly close you will more often then not have a leaking valve.
    Also, the drain pipe from the T&P valve should go to an area where discharge will not be a problem. If you can't run it to a nearby drain then at the very least put a bucket under it. Don't have a drain that runs uphill either.
  15. RoadKing99
    RoadKing99 New Member
    Apr 5, 2011
    New Hampshire
    I had the same water heater installed a few months before you did...about 2 months ago I noticed the bottom of the copper drain pipe turning green and saw what looked like dried water stains on the floor. I stuck my finger in the pipe and it was wet...so like condensation was running down the pipe but not a decent water flow. I do have a closed system with the check valve at the water main but I also have an expansion tank installed on the cold water main.
    So I opened up the relief valve and a bunch of murky water came out.....and like was posted above, you need to really open them up because after I "cracked" it a few times I got a pretty good drip going rather than the slow condensation I was getting before. So I opened it up all the way and that stopped the steady drip........but now I am back to less than 3/4 of a teaspoon over a 24 hour period.
    My situation sounds very similar to yours other than the amount of water....
    Based on this info does this sound like the valve working as it should or perhaps a defective valve like the OP had? Right around same time frame give or take a couple of months on same brand and heater
  16. jadnashua
    The valve should only open under three situations: you manually open it, the pressure is too high, the temperature is too high. ANY other reason means it should be replaced. I'd double-check the expansion tank, it could be shot, allowing the pressure to rise. The tank should essentially be full of air. If it thumps like it is full of water, it is probably shot.
  17. Redwood
    Redwood Master Plumber
    Dec 15, 2007
    Service Plumber
    Maybe if he didn't have the installing plumber coming back out we would have gotten into the diagnostics....
    Your wisdom or, lack thereof never ceases to amaze me...
  18. ballvalve
    Dec 28, 2009
    I am amazed at your lack of ability to diagnose a problem when all the needed information is before you.
    He needed to change his T&P valve FIRST, before all of the typical backyard mechanics "lets change and add parts and see if we fix the problem" but with the added stupidity of not starting with the actual LEAKING part.
    "Hey! the T&P drips after 10 years - lets add a expansion tank to fix it!!"
    Calling an average plumber is akin to heading to a root canal without novacaine. And the odds of a true repair are about like slot machine win rates.
    I'll give Terry an exception.
    Someone might have mentioned that his valve piping also need to be re-routed to a drain or outdoors, and not to his wooden floor.
    This guy got it right. NOT a plumber.
    Get a drop of wisdom and read the entire thread before shooting from the hip.
  19. Terry
    Aug 17, 2004
    The T&P is the first thing replaced. Especially if it had been fine originally.
    If the water meter had been changed out to a check valve version, then an expansion tank would be needed.
    I've seen some homes where the street pressure was 120 PSI.
    With those homes, I add a pressure reducing valve on the incoming cold.
  20. RoadKing99
    Apr 5, 2011
    New Hampshire
    While he was here fixing flange on my toilet he also swapped out the T&P. So far so good and no drips over the past few hours. Said he ends up changing the T&P quite frequently on the B&W heaters he installs for a Watts one. He checked the expansion tank first and added a little air to it to get it to 55 psi I think.
    I just picked up a J horn with a check valve in it from the town water department. I'm going to have him replace the original j horn that has been giving me some leaking problems off and on for the past 6 years or so where they attach to my copper pipes. Plus this will have a ball valve rather than the crummy spigot type that never really killed the main completely anyways and seemed to leak a bit. Just the shock of the water being turned off and on can make it leak at the connections. Thank God for mineral deposits I guess
    If you find a good plumber you trust and does good work they are worth their weight and gold and nine times out of 10 they do better work and are less expensive than the guys a box store will send out....never again!
  21. Gary Swart
    Sep 1, 2004
    Yakima WA
    You really should have zero water coming out of the T/P. I'd suggest you flush it some more, but if it continues to seep, get a new valve. They are cheap and easy to change.
Similar Threads: leaking temp/relief
Water Heater Forum, Tanks Water Heater Leaking from the bottom. Feb 5, 2017
Water Heater Forum, Tanks Sounds like pop off valve leaking.... Dec 8, 2016
Water Heater Forum, Tanks Leaking stainless braided water heater hose. Dec 5, 2016
Water Heater Forum, Tanks New T&P valves on water heater leaking, pressure driven from 65 to 165psi Aug 29, 2016
Water Heater Forum, Tanks What else could it be: indirect hot water heater leaking? Aug 17, 2016