leaking backflow preventer

Discussion in 'HVAC Heating & Cooling' started by edsdad, May 24, 2007.

  1. edsdad

    edsdad New Member

    Messages:
    4
    Have 4-zone h.w. baseboard system. Hydro-Therm furnace piped according instructions has worked fine for 15 years. Recently, the backflow prev. atmospheric vent began to discharge a small but significant amount of water. City w.p. is 60psi (regulated). Supply goes to backflow preventer > auto fill/regulator > furnace. There is also an exp. tank in the loop (new). All the parts listed are new, Watts brand. After new backflow prev. installed, water flow from vent has been reduced but not stopped; dripping steadily. Furnace pressure when firing is high, 16-18 lbs. Hydro-Therm support agrees operating pressure is high but had no real solution to offer.
  2. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Messages:
    21,809
    Location:
    New England
    The expansion tanks usually come precharged reasonably close to where they should be, but you might want to check. To do that, you have to drain enough water out to relieve the pressure, then you can check the air pressure. It should be around 15 pounds. If it isn't, add some. Is the pressure-relief valve new, too? They can wear out or get sticky when they get old.
  3. edsdad

    edsdad New Member

    Messages:
    4
    leaking b.f. prev

    Tank was installed new after the leak started but I had checked the pressure anyway just to be sure. It was at 24 lbs. Thanks - will change relief valve just in case.
  4. CHH

    CHH New Member

    Messages:
    225
    Location:
    Denver, CO
    AIUI, the expansion tank pressure should be approximately equal to the system operating pressure. Also, typically gauges might not be (probably aren't?) calibrated so some error (difference or variation) might be expected.

    On the vent discharge: There is water coming out of the vent and you've changed everyting but the vent. Water continues to come out of the vent. When is the vent going to be tested/changed?
  5. edsdad

    edsdad New Member

    Messages:
    4
    Thanks, CHH. I should have been more clear. The leak is from the atmospheric vent on the b.f. preventer, not the pressure relief valve on the boiler. Today the leak seems to have stopped on its own, no thanks to me.
  6. CHH

    CHH New Member

    Messages:
    225
    Location:
    Denver, CO
    When I reread your initial post, its clearly stated that the vent was on the backflow preventer. I just read "vent" and assumed it was the system vent. My mistake.

    Glad to hear the drip cleared up.
Similar Threads: leaking backflow
Forum Title Date
HVAC Heating & Cooling Help! Exchanger on Pool Heat Pump Leaking! Mar 8, 2014
HVAC Heating & Cooling Beckett Oil Bruner Leaking Oil From The Bottom Of The Plastic Case ??? Mar 1, 2011
HVAC Heating & Cooling PVC Pipe Connected To Metal Drip Pan is Leaking Aug 15, 2010
HVAC Heating & Cooling Leaking Weil MCClane Boiler Feb 7, 2009
HVAC Heating & Cooling Island range hood still leaking Nov 21, 2008

Share This Page