Laundry Room Wiring - Did I goof
Discussion in 'Electrical Forum discussion & Blog' started by devans175, Dec 5, 2007.
  1. devans175
    devans175 New Member
    Sep 18, 2006
    USAF
    Maryland
    I'm building a new laundry room and I want to make sure I didn't mess up the wiring. There was an existing 12/2 cable coming off of a 20 amp breaker. There was nothing but a flourecent light connected to it. I spliced into it with several runs of 14/2 cable. There will be 3 flourescent lights, a very small bathroom fan and 2 receptacles. The only thing that will be plugged into the recepts is a steam iron. The lights are on one branch and the recepts ware on a separate branch. Did I screw up?
  2. 480sparky
    480sparky In the Trades
    Oct 8, 2007
    Electrical Contractor
    You cannot have 14-ga wire on a 20-a breaker.
  4. Cass
    Cass Plumber
    Nov 12, 2005
    You must remove all the 14/2 wireing and change it to 12/2.
    Why did you use 14/2?
  5. Speedy Petey
    Speedy Petey Licensed Electrical Contractor
    Jun 16, 2007
    NY State, USA
    Yeah. And a steam iron is one of the heaviest draw items in your home.
    Remove the 14 and install the proper size wire. ALL receptacles in a laundry room must be #12 wire and 20A circuits.
    You say a bath fan? Does this mean you are also feeding a bathroom? If so the bath receptacles CANNOT share a circuit with the laundry room.
    There are plenty of codes regarding these rooms. I'd study up on them before going ANY further.
  6. devans175
    Sep 18, 2006
    USAF
    Maryland
    I just wasn't paying attention. I'm used to seeing 12/2 cable as yellow. The existing cable was kind of an off white. I just happened to look at the markings and saw it was 12/2. I was also surprised when I saw how much current an iron draws, that's when I got concerned and decided I should ask.
    Lesson Learned. I'm going to split the lights off onto a 14/2 circuit and re-wire the recepts. Thanks!!
  7. Cass
    Cass Plumber
    Nov 12, 2005
    The scary thing about this is all the DIYrs that will do this and not ask any one and then there will be a fire and possibly loss of life.
  8. Ian Gills
    Jul 24, 2007
    USA
    Which is why, as a DIYer, I am only going to run 12 gauge wire now, even on 15 amp circuits. It will make any upgrade (by me or someone else down the line), to 20 amps easier and potentially safer (if they overlook the wiring).
    Obviously wiring for 30 amp (10 gauge), 40 amp (8 gauge) and 50 amp (6 gauge) circuits is a different beast, I am just talking small appliance circuits here.
  9. Mikey
    Nov 8, 2005
    Consumer
    Hansville, Washington
    It's also cheaper to buy 12-2 250' at a time than it is to buy the odd small chunk of 14-2 as well, I think.
    I'm helping a neighbor rewire a garage apartment, and he goes by the cable color also. He's going to be in real trouble if the colors change in the future. I taught him about the markings but it's easier for him to just think "white for lighting" and "yellow for receptacles". We opted for the 14-2 because he has a LOT of lighting and smoke detector circuit cable requirement, justifying the 250' roll of 14-2 also.
  10. Chris75
    Chris75 Electrician
    Aug 12, 2007
    Electrician
    Litchfield, CT
    Speedy, I don't see in the code where ALL receptacles in a laundry need to be 20amp, Your required at least ONE 20amp laundry circuit, which is allowed to supply other receptacles in the laundry area, but I dont see where ALL of the receptacles MUST be on the 20amp circuit...
  11. Speedy Petey
    Jun 16, 2007
    NY State, USA
    See 210.11(C)(2). It is the exact same wording as for the required (minimum) two small appliance circuits in a kitchen.
    You gonna install 15 amp receptacle circuits in a kitchen too? :p
    210.11 Branch Circuits Required
    (C) Dwelling Units
    (1) Small-Appliance Branch Circuits
    In addition to the number of branch circuits required by other parts of this section, two or more 20-ampere small-appliance branch circuits shall be provided for all receptacle outlets specified by 210.52(B).
    (2) Laundry Branch Circuits In addition to the number of branch circuits required by other parts of this section, at least one additional 20-ampere branch circuit shall be provided to supply the laundry receptacle outlet(s) required by 210.52(F). This circuit shall have no other outlets.
    (3) Bathroom Branch Circuits In addition to the number of branch circuits required by other parts of this section, at least one 20-ampere branch circuit shall be provided to supply bathroom receptacle outlet(s). Such circuits shall have no other outlets.
  12. 480sparky
    Oct 8, 2007
    No, because of 210.52(B)(1) and (3).
    But there is no requirement, as Chris75 says, that all the laundry receptacles be on the 20a laundry circuit. You can put the 210.11(C)(2)-required 20a laundry circuit behind the laundry pair, and then have as many other receptacles on 15a circuit(s) as your heart desires.
  13. Speedy Petey
    Jun 16, 2007
    NY State, USA
    All I can say is I disagree. I have really never heard of this being interpreted any other way.
    This is of course for a room/area specifically designated as the "laundry".
  14. Chris75
    Chris75 Electrician
    Aug 12, 2007
    Electrician
    Litchfield, CT
    Your more than welcome to your opinion... ;):D
  15. Alectrician
    Alectrician DIY Senior Member
    Jun 15, 2007
    That's what I thought but I read this in another post.
    Again, I am confused.
  16. Chris75
    Chris75 Electrician
    Aug 12, 2007
    Electrician
    Litchfield, CT
    What exactly are you confused on? Did you read the exception?
  17. BrianJohn
    BrianJohn DIY Senior Member
    Jun 22, 2007
    VA
    For reasons I do not need to go into here except to say on commercial jobs I tell electricians ignore colors and use a rotation meter, I would tell the DIYer.
    IGNORE colors with the exception of green, white (In most cases) jacket color has no meaning use and may vary from manufacture to manufacture. LOOK at the conductor size and as DIYers I would rely on the actual AWG number on the conductor jacket, not on your ability to assume the size by visual inspection.
  18. Speedy Petey
    Jun 16, 2007
    NY State, USA
    Try: 210.11(C)(3) Exc.
  19. Mikey
    Nov 8, 2005
    Consumer
    While rummaging around in 210.23, I see they define "Cord-and-Plug-Connected Equipment Not Fastened in Place" and "Utilization Equipment Fastened in Place". How would you treat Cord-and-Plug-Connected Equipment Fastened in Place, such as a wall-mounted hair dryer? It would seem that the fastening-in-place is what matters, but that would mean my 1500W wall-mounted hair dryers couldn't be plugged into 20A receptacles on circuits where an electric toothbrush, say, was also plugged in. 210.23(A)(2).
  20. Alectrician
    Jun 15, 2007
    I only read the quotes I posted here.
  21. Chris75
    Chris75 Electrician
    Aug 12, 2007
    Electrician
    Litchfield, CT
    How does this thread go from required laundry receptacle, to equipment fastened in place?
Similar Threads: Laundry Room
Electrical Forum discussion & Blog Dedicated outlet for freezer in laundry room = AFCI? Jun 30, 2016
Electrical Forum discussion & Blog Laundry in bathroom, GFI required? Dec 25, 2007
Electrical Forum discussion & Blog Overhead Light -- not kitchen, bath or laundry. Apr 15, 2015
Electrical Forum discussion & Blog laundry: washing-machine clearance from switches Apr 6, 2010
Electrical Forum discussion & Blog Bathroom remodel code question Jun 7, 2016