    Here are a couple pictures of the plumbing for my water closet. (One is dry fit and the other shows it installed). Does this look like it's vented this properly? (The vent pipe will extend 4-5' farther up before it turns.)
    [​IMG][​IMG]
    Thanks in advance!
    Last edited: Feb 14, 2010
  2. cacher_chick

    cacher_chick Test, Don't Guess!

    Messages:
    3,250
    Location:
    Land of Cheese
    A vent cannot run horizontally until it is a minimum of 6" above the flood rim of the highest fixture.
  3. jimbo

    jimbo Plumber

    Messages:
    8,997
    Location:
    San Diego
    Unfortunately that is a VERY BIG NO. That fails inspeciton for the very real reason that such a horizontal vent would very soon be clogged with waste.
  4. mjsmith0

    mjsmith0 New Member

    Messages:
    27
    Location:
    Los Angeles, CA
    Last edited: Feb 14, 2010
  5. jc60618

    jc60618 DIY Junior Member

    Messages:
    88
    Location:
    Chicago
    The last illustration would pass inspection in Chicago, I dont know about your area.The pictures you posted before wouldnt because you had those two fiitings raising the quarter bend above the vent. But like I said this last illustration would pass in Chicago. We often vent suspended toilets, p-traps or showers this way.
  6. mjsmith0

    mjsmith0 New Member

    Messages:
    27
    Location:
    Los Angeles, CA
    Gotcha. It makes sense to me now. Probably should have realized that before. Thanks!
  7. shacko

    shacko Master Plumber-Gas Fitter

    Messages:
    561
    Location:
    Rosedale, Md
    Under the UPC you can run a flat vent the way it's shown, you just have to add a clean-out on the vent where it comes up in the wall.
  8. mjsmith0

    mjsmith0 New Member

    Messages:
    27
    Location:
    Los Angeles, CA
    Another idea

    How about this? Would this work and pass inspection? (The sanitary tee is rotated 45 degrees around the horizontal.)
    [​IMG]
    Last edited: Feb 14, 2010
  9. nhmaster

    nhmaster Master Plumber

    Messages:
    3,189
    Location:
    S. Maine
    Nope, 2 reasons. can't lay a san tee on its side and your vent off the back of it is still flat. Re-think the whole thing. What code are you under? If it's IPC your vent to water closet distance is unlimited and it may be far better to wet vent the whole lav throught the lav.
  10. mjsmith0

    mjsmith0 New Member

    Messages:
    27
    Location:
    Los Angeles, CA
    One last try

    Here is a variation on that design that would fit in the space I have. It is somewhat like the design I found on DIY site I showed above, but with a twist (literally!) I wonder if its too much of a pretzel?
    [​IMG][​IMG]
    Thanks everyone for your patience and help while I try to figure this out!
    Last edited: Feb 14, 2010
  11. nhmaster

    nhmaster Master Plumber

    Messages:
    3,189
    Location:
    S. Maine
    Nope, you still have a flat vent there. All vent piping must rise vertically.
  12. krow

    krow Plumber

    Messages:
    906
    Location:
    Ontario, Canada
    Its being wet vented from what I see. The only issue that I see is that you have too many bends before the vent
  13. mjsmith0

    mjsmith0 New Member

    Messages:
    27
    Location:
    Los Angeles, CA
    If the water closet distance is unlimited, can I do something like this. (This is a picture that show more or less how the whole system is designed.)
    [​IMG]
    Last edited: Feb 14, 2010
  14. nhmaster

    nhmaster Master Plumber

    Messages:
    3,189
    Location:
    S. Maine
    Krow, that looks like a clean out there, not a san tee.
Similar Threads: water closet
Forum Title Date
Plumbing Forum, Professional & DIY Advice Water Closet to Vent stack ? Jun 28, 2014
Plumbing Forum, Professional & DIY Advice Wet vent entire bathroom where water closet at end of run Dec 18, 2012
Plumbing Forum, Professional & DIY Advice Vent size for 3" horizontal drain from water closet Aug 6, 2011
Plumbing Forum, Professional & DIY Advice Question about my Wet Vent on my Water Closet. Jun 29, 2010
Plumbing Forum, Professional & DIY Advice water closet/flushvalve question Feb 22, 2010

Share This Page