This is the second drain in a month I've seen like this. Is it legal?

drain.jpg
 
Last edited by a moderator:

ckl111

Home Builder
Messages
71
Reaction score
2
Points
8
Location
Ontario
Assuming that the drain line is properly vented in the wall, is there a problem with a long tailpiece connected to a low p-trap?

I can only guess that it was installed like that for looks but I don't know how it ever passed inspection. This was in a two year old house so I would think it was done by the original "plumber".
 
Last edited:

Terry

The Plumbing Wizard
Staff member
Messages
29,946
Reaction score
3,460
Points
113
Location
Bothell, Washington
Website
terrylove.com
In that situation, the longer tail piece is the way to go. Raising the p-trap above the vent like that creates a siphon of the trap, leaving it dry.
The purpose of the trap, is to have a water seal against sewer gas in the home.
Put the p-trap in-line with the vent, and add more tailpiece.
Or...cut the wall and raise the santee in the wall.
 