Ok, the information from the Home Energy assessment is in. The blower test determined the building shell leakage to be 2816 CFM50.
Does this information solidify the choice for TT prestige trimax series 60 solo with an input modulation of 16 to 60K BTU/hr?

Regards,

Alexander

Blower door tests give you the order of magnitude, aren't a precise way of determining the infiltration losses since it actually matters where those leaks are. (I hope you chased around during the test and figured out where the worst leaks are so you can remediate?) 2816 cfm/50 isn't super tight. It's also not super leaky about 2 air exchanges per hour, but it's usually cost effective to improve upon that a bit if you found the leakage paths. At 1500cfm/50 and lower the leakage is often harder to find and fix.

Using really crude "N-factor" modeling, in your area you can divide the cfm/50 by 17-20 for the max infiltration rates to expect. So if we divide 2816 by 17 (the worst case) you're looking at 166cfm infiltration in a high wind, which is 9960 cubic feet per hour. At a delta-T of 60F (10F outside, 70F inside) the dumb heat loss number that adds up to is 9960c.f. x 60F x 0.018BTU/c.f. per degreeF= 10,756 BTU/hr.

In reality it's literally never that high, since there's a "heat exchanger effect" along the infiltration & exfiltration paths, but it might be as much as half that figure- call it 5K. To be the full 10,756 BTU/hr requires that the leakage paths be large and low-impedance, so that the volumes of air entering the innermost skin is truly at the outdoor temperature, and the air leaving the outermost skin of the building is at the interior air temperature. It's still reasonable to go with a Solo 60, and continue air sealing.

The 115KBTU/hr IBC is really extreme overkill here, but if the installer seems competent on the system design, it'll probably give reasonalble service, and the boiler & system should be tweakable to modulate most of the winter.
 

AlexanderNY

New Member
Messages
17
Reaction score
0
Points
0
Location
NY
Would a 22 Gallon Buffer tank be large enough to prevent short cycling with a boiler with a minimum output of 20K Btuh and 2 mirco zones?

zone 1: 34 feet fine tube baseboard.
zone 2: 30 feet fine tube baseboard.

Regards,

AlexanderNY
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
Probably. Do the math. 22 gallons at 8.34lbs/gallon adds 183lbs of water to the system. You need to figure out how much else there is on that loop.

20KBTU/hr is 333 BTU/minute. If we assume you get 5F of hysteresis around the outdoor-reset setpoint it takes 5F x 183lbs= 915 BTUs to slew that much, which takes 915/333= 2 minutes 45 seconds, even if you assumed the rest of the system mass was zero, and the fin tube emitted zero.

It's safe to say that you'll be getting 3+ minute of burns out of it even in worst case conditions if you tweak in the reset curves & pumping rates, etc, which is OK for a low-mass boiler.
 

AlexanderNY

New Member
Messages
17
Reaction score
0
Points
0
Location
NY
In the interest of full disclosure, we ended up with the following system:

1. IBC SL 20-115, a high efficiency modulating boiler with outdoor reset control,
2. a 40 Gallon Domestic hot water tank.
3. a 22 Gallon buffer tank.

The buffer tank is used to add thermal mass to smaller baseboard fine-tube baseboard zones.

IMG_1075.jpg
 