Installing a washer drain 1 ft from main stack - is vent necessary?

Users who are viewing this thread

John2.0

New Member
Messages
7
Reaction score
0
Points
1
Location
Iowa
I assume technically it's required but I can't see why it is necessary. It's on the uppermost floor and will be the highest fixture draining into the stack, which penetrates the roof 8-10 ft above. If I can even squeeze a vent connection between the p-trap and the tie-in, how is it actually necessary?
 

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
If is is the highest connected drain on the stack, then no, it does not require a seperate vent.

You may be creating a different problem though, if the fixture below that is not re-vented. The highest drain connection on the stack is the ONLY fixture which can use the stack vent without being re-vented.

dwv_b2.jpg
 
Last edited by a moderator:

John2.0

New Member
Messages
7
Reaction score
0
Points
1
Location
Iowa
If is is the highest connected drain on the stack, then no, it does not require a seperate vent.

You may be creating a different problem though, if the fixture below that is not re-vented. The highest drain connection on the stack is the ONLY fixture which can use the stack vent without being re-vented.

dwv_b2.jpg

Ahh, yes, something I did not think of but makes perfect sense. Thank you! A few feet below the proposed tie-in is a pipe running to a toilet (about 3' away) which also goes on to a tub (an additional 3-4' away), neither of which are vented. Looks like I'll have to address this, too.
 