install coin vent at the end of the CI baseboard

Users who are viewing this thread

lmei007

Member
Messages
183
Reaction score
0
Points
16
Location
Maryland
I have some snug CI baseboards. I cannot use the desiged position for the coin vents. So i have to use the end 3/4" opening for the coin vents which is 1/8", I think.

Then i need a adapter for this installation. By searching online, this Steel NPTF Pipe Hex Reducer Bushing is the only one I found.

My question is the steel is good to be used with CI? do you have better adapter?
 

hj

Master Plumber
Messages
33,599
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
It's the only bushing you can purchase, other than brass. But why a "coin vent"? They are okay for a large radiator with a lot of water in it, but a baseboard has such small capacity that even a small amount of air can cause a problem. That is why we use automatic vents on baseboard, besides being more convenient.
 