Indirect Water Heater Not Calling for Heat

Discussion in 'Plumbing Forum, Professional & DIY Advice, Tips & ' started by robertr4836, Feb 22, 2009.

  1. robertr4836

    robertr4836 New Member

    Messages:
    1
    Location:
    New England USA
    Hi,

    I have an indirect fired water heater. A few weeks ago we ran out of hot water which had never happened before.

    I checked and even though the tank needed hot water the boiler was not firing. I reset the boiler and everything seemed to be fine.

    Yesterday we ran out of hot water again and the same thing had happened, the water heater was not calling for heat from the boiler. I reset the boiler again and it seems to be working but I want to get this taken care of.

    I figure it's the Honeywell controler that's the problem but I am very new to owning a house (had a condo before and I never had to deal with these things). Do I call an electrician, a plumber or the boiler service techs?

    Thanks for any response.

    Robert
  2. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Messages:
    21,896
    Location:
    New England
    The sensor that tells the boiler to turn on may be bad or possibly the leads came loose either by getting knocked or just multiple heating/cooling cycles if they weren't tightened down properly.

    On most, you can test the sensor with a multimeter on ohms scale. The specs will say what the resistance across the sensor should be at any temperature. The resistance changes as the temperature changes. If the sensor is working, then the control in the boiler may be shot. If the sensor is not working, replacement is normally easy.

    A good HVAC boiler guy should be able to diagnose this, but you may want to try yourself. Don't do resistance checks with power on, and you really need to actually disconnect the leads to get an accurate reading.
  3. kingsotall

    kingsotall Plunger/TurdPuncher

    In these neck of the woods you're better off with a plumber. I should know, I work with him 4 days out of the week. There's a thread just started that could probably go have plumber vs. tinner for boilers.
Similar Threads: Indirect Water
Forum Title Date
Plumbing Forum, Professional & DIY Advice, Tips & Zone valve or its own circulator for an indirect water heater? Jan 20, 2011
Plumbing Forum, Professional & DIY Advice, Tips & indirect water heater question Jan 19, 2009
Plumbing Forum, Professional & DIY Advice, Tips & Indirect Fired Water Heater Troubleshooting Help Nov 2, 2008
Plumbing Forum, Professional & DIY Advice, Tips & indirect water heater Dec 26, 2007
Plumbing Forum, Professional & DIY Advice, Tips & What type indirect water heater? Aug 27, 2006

Share This Page