Incorrect boiler pressure relief valve installed

Users who are viewing this thread

masterplummer

New Member
Messages
1
Reaction score
0
Points
1
Location
Amherst, Massachusetts
Relief valve was leaking and was badly corroded, so I planned to replace it.

Got the new one on, and it would trip when I tried to refill the system. Discovered that I had inadvertently got a relief valve only rated for 15psi instead of 30psi like the old one.

So my question is, what is the risk in leaving the current 15psi valve on until I can get a 30psi one? Is my boiler under filled with water; do I risk it overheating?
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
Even if you pre-charged the system and expansion tank to 9-10 psi there's a good chance it could exceed 15 psi, spitting water. Some low-mass boilers really need 12 psi+ to avoid flash boil, but you'll likely be able to hear the sizzle & bang well before there was actual damage being done.
 