What is the best product to use for insulating in-slab pex? Rfoil bubble or EPS Foam? Anyone have any experience with either?
Thanks for your help.
Rolfsi
 

Bob NH

In the Trades
Messages
3,310
Reaction score
9
Points
0
Location
New Hampshire
You don't usually insulate the PEX. You insulate between the slab and the ground and around the perimeter with a good closed-cell foam designed for the purpose. Then the heating tubes are usually installed about 1/3 of the thickness of the slab from the top.

The fact that you are asking that question here suggests that you need more help that we can give you, because we don't know the details of your situation. A good design requires enough information to do the design and analysis.

You need to get a good thermal design of the whole slab system. If you get it wrong you end up spending a lot of $energy$ to heat the earth. Then, when the energy costs become unbearable you are forced to abandon an expensive system and replace it with another expensive system that doesn't send a lot of BTUs toward the center of the earth where it is not needed.
 

Rolfsi

New Member
Messages
10
Reaction score
0
Points
0
Location
Lacon Illinois
thanks

Bob:
Thanks for your help. I am assuming your answer to the question is EPS ridgid board? I would prefer to do the PEX aspect of it myself and leave the manifold, pumps, boiler, etc. up to a plumber. Any suggestions?
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
hear

Why would you want to do the most important, and the one that could be screwed up the easiest, and leave the easy part to the professional. If you do not install the PEX properly, or have the right PEX, you will have a bad system, no matter how good the plumber installs the rest of it.
 

Bill Arden

Computer Programmer
Messages
584
Reaction score
0
Points
0
Location
MN, USA
Website
www.billarden.com
I have 2 inch yellow foam under the slab and 2 inch yellow foam up the outside of the slab.

Edit: if you have a high water table, you will want 4 inches of ridged closed cell foam.
 
Last edited:

Alternety

Like an engineer
Messages
768
Reaction score
0
Points
16
Location
Washington
And you should put in and overlapped at the joints (glued is best) poly vapor barrier.

You should look at some radiant heating books and figure out what size pipe (1/2" is pretty common). Make sure it has an oxygen barrier, layed out in the proper spacing and pattern, equal length loops if possible (makes balancing easier), manifold locations planned, zones figured out if you are doing that. It is not rocket science, but it does require knowledge.

Web site for slantfin has a free heating loss calculator.
 

Bill Arden

Computer Programmer
Messages
584
Reaction score
0
Points
0
Location
MN, USA
Website
www.billarden.com
I was lazy and let the heating contractor work all that out for the slab.

This just leaves the easy parts that can be changed if needed.
 

Seaneys

New Member
Messages
192
Reaction score
0
Points
0
Location
Chicago Suburbs
What is the best product to use for insulating in-slab pex? Rfoil bubble or EPS Foam? Anyone have any experience with either?
Thanks for your help.
Rolfsi

I don't know if it is best, but I used 2" pink foam and a vapor barrier.

Bob is right - you want really research this (especially if you live in a cold climate). As I recall, there are several good sites on the web.

Steve
 

Rolfsi

New Member
Messages
10
Reaction score
0
Points
0
Location
Lacon Illinois
radiant heat

Just finished getting it installed and boy is it neat. Used a Munchkin contender boiler and it is really a neat system.
 