I need help bleeding air out of my 3 zone residential boiler

Users who are viewing this thread

Pauley Wallnutz

New Member
Messages
1
Reaction score
0
Points
1
Location
New York
Hello Terry Et al-
My system is percolating loudly 24/7 and it's driving me insane! Can someone walk me through bleeding the air out of my boiler? There are 3 Honeywell zone valves and a Bell&Gosset pump driving the system. Thank you very much!
 

Attachments

  • 100_0507.JPG
    100_0507.JPG
    65.3 KB · Views: 1,107
  • 100_0508.JPG
    100_0508.JPG
    81.6 KB · Views: 904
  • 100_0509.JPG
    100_0509.JPG
    73.6 KB · Views: 772
  • 100_0510.JPG
    100_0510.JPG
    75.3 KB · Views: 755
  • 100_0511.JPG
    100_0511.JPG
    62.9 KB · Views: 740
  • 100_0513.JPG
    100_0513.JPG
    56.8 KB · Views: 755

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
The best place to bleed the system is at the highest zone/radiator in the house, not at the boiler. First make sure the system pressure is at least 12-15psi, then go upstairs and look for the bleeder valves on the radiators/baseboards. (On baseboards it'll be under one of the end caps.) If you crack the bleeder and you can pull a quart or more out without any hissing or spitting, it's probably not an air problem.

You have an air vent right at the top of the boiler- the bronze thing on the tee where it branches off to the expansion tank, and even though it's not ideally placed, over time it should purge air from the system.

The expansion tank installation is not exactly a in installation of great beauty, but I've seen worse. By having it out 18" on a pipe it's less effective at dampening pump vibration, but it is also likely to create a leak point (or even a sudden catastrophic break) on that tee over time due to the large moment arm. That's a lot of mechanical stress to put on that tee!

The expansion tank SHOULD be before the input-end of the pump (the sucky side, not the blowy side) and in the shortest possible stub off the flow channel. Your installation seems to either have the boiler between the expansion tank and pump, and a 90 degree turn just before the pump, which maximizes the turbulence of the water as it enters the pump, OR (more likely) you have the impedance of the radiation loops between the expansion tank and the input to the pump, which is about as bad as it gets. The "percolating" you hear may in fact be cavitation on the pump due to improper expansion tank placement & implementation. This would be good to fix sooner than later, since cavitation will age the pump very rapidly.

0909pm-Sieg-fig1-lg.jpg


The boiler looks almost shiny-new- was it just installed in the past year? If yes, the installer should be on the hook for re-configuring in such a way that it would at least get the gentleman's C pass in Hydronics 101.
 