I have a new softner but???

Discussion in 'Water Softener Forum, problems, installation and r' started by MOVIE GUY, Jan 28, 2010.

  1. MOVIE GUY

    MOVIE GUY New Member

    Messages:
    7
    Location:
    WICHITA
    New softner, with clack 1.25, 10x54 tank, sst-60 resin, but my city water was 8 hardness before softener and now is 1 hardness? Should it not be o hardness?

    Thanks for any and all help.................
  2. Bob999

    Bob999 In the Trades

    Messages:
    448
    Location:
    Pennsylvania
    Generally you should expect to remove almost all hardness--but even using SSt-60 resin there may be very small amounts of hardness leakage--perhaps 1-2 ppm or 0.1 gpg.

    What are you using to measure the hardness?

    What is your maximum flow rate through the softener? Hardness leakange increases with flow rate.

    How do you have the control set up? How often do you regenerate and with what amount of salt? What is your typical daily use of water?
  3. Gary Slusser

    Gary Slusser That's all folks!

    It sounds as if the softener may not be sized correctly and your peak demand flow rate is higher than the constant SFR of the volume of resin. And from your other post about the softener, you probably don't have it programmed right.
  4. Akpsdvan

    Akpsdvan In the Trades

    Messages:
    1,484
    Location:
    Alaska
    Check to make sure that there are no open or partly open valves that would let untreated water cross into the treated side.

    When you did the test the water had been running for how long?
Similar Threads: softner
Forum Title Date
Water Softener Forum, problems, installation and r Help me finalize water softner system May 8, 2014
Water Softener Forum, problems, installation and r Water Softner Reccomendation Apr 3, 2014
Water Softener Forum, problems, installation and r water softner keeps running water like it is recharging Feb 24, 2014
Water Softener Forum, problems, installation and r Some Help with Softner Resin and sizing Feb 24, 2014
Water Softener Forum, problems, installation and r Water Softner sizing and programming Feb 21, 2014

Share This Page