How much $$ Efficient is a new boiler over old
Discussion in 'Boiler Forum' started by chefwong, Dec 8, 2012.
  1. chefwong
    chefwong Member
    Jun 14, 2006
    District of Columbia
    Gas is quite cheaper out here than electric.
    We had the entire house installed with a Mitsubishi Mini Split around 2 years ago.
    It also has *inverter * based heat.
    I have a old boiler - probably close to 70+ years old....
    Went to my neighbors and while she is a single, the plumber who installed her water tank looked like it was 35 Gallons.
    Anyhow, her Boiler is literally 1/5 the size of out current one. Efficiency wise, I'm not sure how that stacks up..
    I don't know how much more efficient it is, but I might as well start exploring it, as I feel like it's got only a couple legs left on this thing.
    I'm not sure whether the cost to replace the boiler outweighs the costs if I just use the Minisplits exclusively.
    Thoughts, suggestions
  2. jadnashua
    A decent mod-con boiler is not cheap to install. It does have the ability to (if setup right) provide more comfortable heat than an old on/off boiler control system. The rated efficiencies will actually vary a fair amount depending on how well they are chosen to match the load and how well the overall system is designed. But, with today's NG prices fairly low, it may not cost that much in efficiency to use an old one verses the install cost of a new one. If there are rebates, that can quickly change the equation. But, in a mild climate and not horrendous electric rates, heat pumps can hold their own, at least in heat output. A boiler may provide better comfort though. Some just do not like the air blowing, and radiation tends to be more even than forced air. A boiler does produce more hot water/faster than an electric WH and at lower costs, so you need to factor that into your overall energy use equation. But, an indirect tank will also cost more than an electric. It will last longer.
  4. Dana
    Dana In the trades
    Jan 14, 2009
    01609
    Oversizing high-mass boilers by more than ~1.6x has a damaging effect on the average operating efficiency. If it's literally 5x oversized (as it might be based on your neighbor's boiler sizing), you can take at least 15% off the steady state efficiency (BTU-out divided by the BTU-in) as an estimate of the as-use AFUE, eg:
    Say your actual design-condion heat load is 40,000BTU/hr, but your boiler has a rated output of 200,000BTU/hr, with 250,000 BTU/hr in for a 80% steady-state efficiency, the true as-used efficiency is not likely to exceed 65% due to high idling losses during the shoulder seasons (even for cold-starting boilers.)
    The greater the degree of oversizing for the actual loads, the worse off you are. AFUE testing is at a duty cycle that presumes 1.6x oversizing and a low operating temperature for minimum idling & cycling losses. Take a look at the regression curves in the appendices for the boilers tested by the Brookhaven Nat'l Labs in this document, and consider how far to the left of the curve you are if the peak load is at the 20% mark (5x oversizing), which puts the average load for the season somewhere in the 8-12% range.
    Then consider that corrosion &/or scale on the heat exchanger plates have knocked on the order of 5% off the steady state efficiency, so that 80% boiler is really 75%, and at 5x oversizing you're getting maybe 60% as-used efficiency.
    Most hydronic boilers at the age of 70 would be struggling to hit better than 50-55% efficiency. If it's a steam boiler it might not even be that good.
    A new right-sized mod-con boiler can deliver north of 90% as-used efficiency, and would be a good investment were the boiler your primary heating source. But in a D.C. climate the mini-splits deliver PHENOMENAL shoulder season efficiency, and pretty-good mid winter efficiency. If the mini-split is handling 75%+ of your heating load or more there's little financial incentive to change, and you may still get better bang/buck out of a programmatic approach to air-sealing and insulating to reduce the load. A new mod-con and heating system tweaks could easily run $8-12K, which buys a lot in terms of air-sealing the basement & attic to kill off stack effect infiltration, and spot-insulating where there are gaps. Most of the older homes in the mid-Atlantic states would leak more than 8 air exchanges at 50 pascals pressure in a blower-door test before an air sealing effort, and if that leakage is concentrated at the basement (foundation sills & band joists are notoriously leaky), and the attic (recessed lights, balloon framing, plumbing & electrical chases & penetrations), the impact on heating energy use is significant.
    Most homes in the mid-Atlantic region also have no foundation-wall insulation, which will account for a double-digit fraction of the heat load & heating fuel use in a multi-story house, often over 20% for a single or 1.5 story house.
    If an equivalent amount of weatherizing can bring the design condition heat load within the output range of the mini-split it may be worth mothballing the hydronic heating system. But if you're committed to hydronic heating, the first and most-important aspect when considering a new boiler is to get the sizing right, with a room-by-room Manual-J or I=B=R type heat loss calculation, base on the realistic 99% outdoor design temperature, with minimal or no oversizing. A right-sized 85-88% sealed combustion cast iron boiler can be a significant cost savings over a mod-con up front, and would still deliver a significant fuel savings below heating with a 5x oversized boiler.
    To calculate your average heating costs with the mini-splits vs an oversized boiler running 65-70% efficiency, we'd need to know your electric rates (total bill divided by the kwh used) and your gas rates (total bill divided by your therms or ccf or decatherms, however it's done under your utility.) Unless your electric rates are significantly higher than the national average or your gas rates lower, it's likely that heating with the mini-splits will be cheaper. No matter what your rates are (barring island community 50cents + electricity) the mini-splits will be almost certainly be cheaper to heat with whenever it's over 40-45F.
  5. BadgerBoilerMN
    BadgerBoilerMN Hydronic Heating Designer
    Mar 4, 2011
    hydronic heating designer/contractor
    Minneapolis
    Your boiler is twice the average age. Go ahead, buy a condensing boiler properly sized and controlled. You will be glad you did. I have both and am glad the heat pump quit working as the temperature dropped outside. But then, I am a ModCon zealot!
  6. jadnashua
    When I last replaced my boiler (a Buderus unit was installed), the old one was supposed to be an 87% efficient unit (the Buderus is spec'ed at up to 94% at the time, I think it's higher today - not sure if they changed the unit or the way it is rated!), my gas bill went down by about 1/3. But, if you take the cost of fuel and the cost of the install, it may not pay off in quite awhile. But, the old unit was becoming difficult to get parts for, and kind of weird in its operation (a Trianco Heatmaker II), so I bit the bullet and changed things out.
  7. Dana
    Dana In the trades
    Jan 14, 2009
    01609
    If he didn't have mini-splits that were up to the task I'd say investing in a mod-con would be "...$$ Efficient..."(which was the question, after all).
    But since the mini-splits are already installe and may already handle the heat load or could with some judicious upgrades on the house for less than a mod-con install, and the annualized heating costs are pretty much a wash, going with the mini-splits and mothballing the beastie-boiler is likely to work out as more "...$$ Efficient...".