    I apologize if this is a stupid question, but I'm having trouble figuring out the answer from my books and code checks, so here goes:

    How far can a vent run horizontal once it get up above your fixtures? For example in the attached picture:

    1) as far as I can tell, Distance "X" needs to be <6 feet

    2) For distance Y and Z, is there limitation before I turn up to the roof, or could I theoretically go across the house?

    A little critic on my plumbing setup would be apprciated as well! Thanks,

    FYI, I'm planning out a full basement bath and bar sink that is across the house from the main stack. I have another stack at the back of the house that I plan to run to, but I believe I need to run a new vent up the nearest wall to the new bath.... I don't think Seattle PLumbing code (UPC) allows side wall venting, which would have been easier.

    Thanks again,
    Nick
     

    Attached Files:

  2. prashster

    prashster New Member

    Joined:
    Dec 7, 2005
    In my town, there is no length limitation on Y, Z. However, both sections must be downward sloping to the drain so that condensate any errant water that finds its way into the system has a place to go. There should be no low points.
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. burdick101

    burdick101 New Member

    Joined:
    Jul 31, 2006
    Thanks for your help. One more follow-up question. Can I change direction on during that long horizontal run (either Y or Z in the previous picture) as long as I keep that 1/4 per foot drop for condensate?

    I'm probably making more trouble for myself and ought to just run a new vent pipe, but fishing it up the interior wall is a real pain.

    Thanks,
    Nick
     
  5. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Joined:
    Sep 2, 2004
    Occupation:
    Retired Systems engineer for defense industry.
    Location:
    New England
    I think you'll find that once you are above the flood plane, as long as you have the slope to allow condensation or rain water from the roof to drain, it really doesn't matter where you go with it.
     
  6. prashster

    prashster New Member

    Joined:
    Dec 7, 2005
    Ditto. Bend me, shape me, any way you want me. As long as you love me, baby, it's all right!
     
  7. Terry

    Terry Administrator Staff Member

    Joined:
    Aug 17, 2004
    Occupation:
    Plumber
    Location:
    Bothell, Washington
    The X measurement with upc code would be from the vent to the flange,(six feet or less)

    The vent horizontal could be 1/3 the vertical.

    So if you had 24 feet of vertical, your horizontal could be 8 feet.
    If you go up a pipe size, there is no limit.
     
  8. burdick101

    burdick101 New Member

    Joined:
    Jul 31, 2006
    I'm sorry, now I think I just got confused. Terry, did you just nix what the others were saying? Perhaps you could point me in the direction of the code far that horizontal vent code?

    Thanks
    Nick
     
  9. burdick101

    burdick101 New Member

    Joined:
    Jul 31, 2006
    Never mind, just found it... UPC 904.2... But it says:

    "904.2 No more than one-third (1/3) of the total
    permitted length, per Table 7-5, of any minimum
    sized vent shall be installed in a horizontal position.

    Exception: When a minimum sized vent is
    increased one (1) pipe size for its entire length,
    the maximum length limitation does not apply."

    Am I mis-reading? This appears to say that it is allowed to be 1/3 the TOTAL length, which for a 2" vent would be 1/3 of 120 feet, or 40 feet.
     
    Last edited: Aug 1, 2006
  10. Terry

    Terry Administrator Staff Member

    Joined:
    Aug 17, 2004
    Occupation:
    Plumber
    Location:
    Bothell, Washington
    That's how it appears to read.

    1/3 of total allowed. That would mean that up to 40 feet of 2" could be horizontal without going up a pipe size.

    I wish I had seen that 10 years ago when I was doing a resturant in Bellevue. The inspector didn't see it that way.

    One third of the allowed lenth is much more than 1/3 of vertical.
     
Similar Threads: vent Horizontal
Forum Title Date
Plumbing Forum, Professional & DIY Advice Venting horizontal offset and diagram question Feb 10, 2015
Plumbing Forum, Professional & DIY Advice Toilets, horizontal wet vents, and end of line cleanouts Jan 2, 2015
Plumbing Forum, Professional & DIY Advice Vent reducer in horizontal position? Jan 2, 2015
Plumbing Forum, Professional & DIY Advice Can I use a horizontal vent pipe? Nov 27, 2014
Plumbing Forum, Professional & DIY Advice What is the maximum length for a horizontal "foot" vent connection under UPC? May 4, 2014

Share This Page